Scorpion90

hi guys when measuring loop
empedans with kt 64 it gives me 2 option by chosing with f1 L-n l-pe which one shoul be used?? Thank you very much..
 
Hi,
If you are testing you should know the answer to this one,
Q1. What would you use L-N for?
Q2. What would you use L-PE for?
Try and answer first before anyone tells you, that way you may be able to understand the principle better,

Regards.
 
when the tester in loop mode .. how can u get psc reading?. i meant to say on loop mode there is option by choosing with f1 l-pe l-n when i choose l-n i get ohm reading sir.. my question is why r we measuring l-n?
 
The KT64 has a rotary dial. The settings are Continuity, Insulation, Loop, PSC/PFC, RCD, Volts. LOOP or EFLI = Earth Fault LOOP Impedance - measured in ohms. PSC or PSCC = Prospective Short circuit Current (L-N) - measure in Amps. PFC or PEFC = Prospective Earth Fault Current (L-PE) - measured in Amps. PFC needs (L-PE) impedance and PSC needs (L-N) impedance to enable them to be measured.
 

Reply to KEWTECH KT64 loop testing.. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K
Hi, All I have a megger LTW325 and fluke 1664FC to measure loop impedance by using high current mode. But both results are quite different...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock