Discuss Kitchen fitters, well more sellers. in the UK Electrical Forum area at ElectriciansForums.net

GBDamo

-
Esteemed
Arms
Reaction score
3,010
Just got back from a work mates foreigner.

Received a panicked phone call from him that a 6mm cooker feed had no earth, indeed it did not.

A bit of chasing up the wall found a chock block in the old cooker point back box and the earth had popped out.

However, I asked the question what he was up to and he explained he was putting two double sockets on the 6mm for the hob, oven and convector/microwave.

Best of luck with that said I???

Feeling charitable I went through the ratings off all the cookers 8Kw, 3Kw & 1.1Kw = 52 A

Point 1, you intend to put a 13A plug on a 32A induction hob?

Point 2, you then intend to add a further 20A of ovens to a circuit protected by a 30A rewirable fuse.

Point 3, these sockets you've added, are they RCD protected?

At this point I did a Dragons Den, "I'm out"


But, the point is his mate, that he's doing the foreigner for is employed by a national kitchen supply and fitting chain who have "designed" this kitchen and its appliances.

The mind boggles.

The poor couple are looking at upwards of a £1000 of electrical work on top of their kitchen cost, with a kitchen half fitted.

Shiny suited sales shisters should be shot.☹☹
 
Splendid example of alliteration right there in the OP!

Incidentally, Tel, there's a new programme on TV where pork is auctioned by one of the Simpsons. It's called "Hams Under The Homer"
do i see a knotted rope dangling from the yardarm?
 
That much presumably as they need a CU change as well?
I reckon so, didn't want to get involved so only briefly looked over things.

Fuse board and cut out in a very cramped corner cupboard.

Rewirable fuse board, no RCDs anywhere, only 5 circuits but couldn't see any bonding, can't see it testing out fault free.

Then there's the modifications required in the kitchen.

Could easily see it topping a grand.
 
Trouble is most kitchen sellers don’t give a rats about the state of the existing wiring.
I used to sub by for a big kitchen firm and we were paid to put in x y z on a price per point and were simply expected to connect onto what ever was already there. I used to find 1mm used to extend cooler circuits on a 30a rewiring fuse and we were explicitly told to connect onto it otherwise we wouldn’t get out our money ...
 

Reply to Kitchen fitters, well more sellers. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Recently a mate had a new kitchen fitted, he's gone for an induction hob and pyrolytic oven, no gas at the property. At 1st fix a single...
Replies
10
Views
4K
Hi Guys New to forum and enjoying reading the threads, all interesting, so.. Looking to re-wire my kitchen due to re-fit and some of you will be...
Replies
64
Views
6K
W
Hi I am new to the forum and would like some expert advice on my kitchen planning and also a sanity check on the maths please. I will be...
Replies
17
Views
2K
WOMick
W
I've been self employed for 4 years and have just had my second ever experience of a bad customer, where I've walked. Rewire of a 2 bed bungalow...
Replies
36
Views
6K
B
Hello all, could I ask your advice and opinion? 18 months ago, I fitted in a new kitchen to my house (built 1994). My friend did some electrical...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock