Discuss KT65DL voltage test compared to Fluke T130 double pole voltage tester voltage test in the UK Electrical Forum area at ElectriciansForums.net

T

The Ghost

So Put a couple of LED panels in new fabricated unit finished install and tested Zs, as you do. Fine on L-N not fine on L-PE, KT65 DL says voltage on earth 79v to be precise(ish?) Ok so just double check with Fluke T130 get 44v. This is present no matter what the state of the lights are i.e. on/off. I am not worried about why the voltage is on there. I repeat I am not worried about why the voltage is there. I am puzzled as to why the discrepancy in voltage is there i.e. KT65DL 79v Fluke T130 44v. The fluke has a digital read out so it is not just the red lights measuring in 25v increments. I have spoken with Kewtech and they say there v. test has never been wrong. And of course it is critical the difference as 50v a.c. being the threshold for hazardous voltage. Then just for fun and to see if it was a phantom/induced voltage I popped the Drummond MTL20 tester across PE to N and it says zippo voltage.
 
what does the wet finger test show? :D:D
 
As it's now after 5pm and I have the first beer in front of me, I'll take bets that you've measured the voltages separately and the delta is (mostly) due to the different internal impedance of the meters when trying to read a ghost voltage. You may prove me wrong by taking the readings simultaneously and then buying me a beer or it can be my shout :)
 
So Put a couple of LED panels in new fabricated unit finished install and tested Zs, as you do. Fine on L-N not fine on L-PE, KT65 DL says voltage on earth 79v to be precise(ish?) Ok so just double check with Fluke T130 get 44v. This is present no matter what the state of the lights are i.e. on/off. I am not worried about why the voltage is on there. I repeat I am not worried about why the voltage is there. I am puzzled as to why the discrepancy in voltage is there i.e. KT65DL 79v Fluke T130 44v. The fluke has a digital read out so it is not just the red lights measuring in 25v increments. I have spoken with Kewtech and they say there v. test has never been wrong. And of course it is critical the difference as 50v a.c. being the threshold for hazardous voltage. Then just for fun and to see if it was a phantom/induced voltage I popped the Drummond MTL20 tester across PE to N and it says zippo voltage.

True RMS is not provided by a 2 pole fluke volt tester.
 

Reply to KT65DL voltage test compared to Fluke T130 double pole voltage tester voltage test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I saw a Fluke 1653B on Gumtree local to me being sold as faulty. Fault was stated as no continuity between 'N' and 'PE' ports on the resistance...
Replies
3
Views
456
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
780
Hi, I would love some help understanding an issue I’m having on a 16mm SWA cable running from the CU in my house to the CU in the shed. I believe...
Replies
15
Views
2K
Spent yesterday morning running a spur in my kitchen from one double socket on the rfc to a new one along the same wall. Original socket is just...
Replies
4
Views
1K
Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock