hodaire

Anyone know what type of driver i would need for 3 x 1w 350 m/A leds wired in series.

person who wired these has dissapeared and i'm trying to finish the job off, been in touch with the manufacturer (targetti) and they want £120 for the driver and reckon delivery will be about 5 weeks, anything i could pick up from a standard wholesaler?
 
What sort of driver do you need ? just a basic driver or one that's dimmable etc? You want to search for a 350mA Constant Current driver - almost any will be suitable for such a small load - I have 15 of them (across 4 channels of DMX control), and even that driver only cost me about £60 :)
 
There are 2 types of LED drivers a constant current and a constant voltage.

Constant current is when the LEDs are in series

Constant voltage is when LEDs are in parallel
 
whats the difference between constant current and constant voltage?
They do exactly what the names imply. One maintains a constant output voltage (current will vary depending on load). The constant current one will have a high output resistance enabling it to maintain a constant current. Usage as Ian has already said.
 

Reply to LED Driver in the Australia area at ElectriciansForums.net

Similar Threads

Hey folks, i work for a relatively small company, but we are doing some big jobs. And right our headache is taking over outdoor lighting...
Replies
4
Views
1K
Hi there, I'm currently working on a project where I'd like to slowly fade the brightness of a series of high brightness RGBW LEDs. Basically...
Replies
3
Views
944
Using these lights (wired in parallel) 6 x 2W is ok to use a 12V constant voltage 16W led driver Aurora AU-LED16T. My question is they are a G4...
Replies
4
Views
2K
Hi, I'm a DIY / home owner that has a bit of wiring knowledge but has not wired LED drivers before. I have a chandelier that has 36 hanging...
Replies
0
Views
1K
Hi, can anyone recommend a dimmable constant voltage driver for a LED strip and any suppliers? Many thanks
Replies
3
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock