nick.appleby

Hi all.

Am trying to replace switches and wall leights and ceiling lights i have identified live and neutral (black and red)but what appears to be the earth is a grey colour also its not wired to the earth terminal but to one of the Com connectors. Does this mean that there is no earth wiring or has it been wired wrong, could really do with a quick response please help

Thanks

Nick
 
It's not a 3 core cable is it.Brown,black and grey:confused:Are they singles or T & E
 
Last edited by a moderator:
Hi all.

Am trying to replace switches and wall leights and ceiling lights i have identified live and neutral (black and red)but what appears to be the earth is a grey colour also its not wired to the earth terminal but to one of the Com connectors. Does this mean that there is no earth wiring or has it been wired wrong, could really do with a quick response please help

Thanks

Nick


Nick

Please be aware of what your doing, if unsure leave it for now, await replys or provide further info
Better safe then sorry.

Ash
 
Im sure i have seen the black in T&E turn greyish near the terminal, which looked like signs of overheating.

It most certainly sounds like no cpc on the lighting circuit.

However, in olden days, they used to twist the cpc's together and stuff them up in the ceiling behind the wooden pendant mount.
 
Last edited by a moderator:
if there is no cpc can i still replace light fitting etc, there are platic patress boxes to all sockets and switches i have bought metal switches, also the light pendant is metal ??? thanks everyone
 
if there is no cpc can i still replace light fitting etc, there are platic patress boxes to all sockets and switches i have bought metal switches, also the light pendant is metal ??? thanks everyone

If there is no earth present you need to get it rewired.

And dont fit ANY metal switches or fittings!!!!!
 
if there is no cpc can i still replace light fitting etc, there are platic patress boxes to all sockets and switches i have bought metal switches, also the light pendant is metal ??? thanks everyone
Are the wall fittings metal.If they are they need to be earthed mate:)
 
if i dont use any metal fitting ie switches sockets or pendants and use plastic will it be ok to use plastic without the cpc many thanks eveyone first time here and the advice is brilliant cant thank you enough

it definetly needs a re-wire and your right about the board the prblem is the current fitting are metal just want to make safe before the re-wire
 
Last edited by a moderator:
if i dont use any metal fitting ie switches sockets or pendants and use plastic will it be ok to use plastic without the cpc many thanks eveyone first time here and the advice is brilliant cant thank you enough
In my opinion mate,i would get the property rewired.Is it your property or are you doing work there.
 
be care full there may be no earth. I hacve see the old wiring in houses 30 years + where all lights are done in 1.5 double insulated singles and going back to a big joint box.
 

Reply to lighting circuit identifying earth on old wires in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock