Discuss Lights dimming in the Industrial Electricians' Talk area at ElectriciansForums.net

Have you tested the circuits in question? Have you visually inspected all terminations including upstream? I'd start with those.
 
Checked all terminations at CU and on shower circuit. Voltage drop at cu is 10V. I also noticed when the ring main was turned on that the lights dimmed, but not as much as when the shower is turned on
 
Check voltage is within statutory (253 - 216) volts with the shower turned on. Check all up stream terminatations, check for signs of buring. If the connections are ok and still outside the limits, phone the DNO, on a back of an envlope calculation 300 watts are being lost in that resistance. If this is a new problem phone the DNO.
 
Also if it's one of those ridiculous 10.5 -10.8kW showers I'd say it's perfectly normal to notice the lights dimming slightly when it fires up.
 
How old is the house? Loose neutral in joint box under pavement maybe. Daz
 
sudden unrush of current from an electric shower can cause sudden dip of lights. The same with all heavy loads such as a kettle.

Hope this helps.
 
Last edited by a moderator:

Reply to Lights dimming in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Kitchen led lights have all of a sudden dimmed by about 30% no dimmer in the system. There are 2 switches for this set of lights. Regardless of...
Replies
2
Views
828
Hi All, Pretty comfortable with wiring lighting until I came across needing to install 2 way dimming with a Retractive switch. I didn’t even know...
Replies
3
Views
809
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K
Hi, client wants lights dimmed at 3 separate points controlling one light, I don’t think it’s possible without a smart system etc, any thoughts?
Replies
6
Views
818
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
198

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock