Discuss Like for like replacement and MWC in the UK Electrical Forum area at ElectriciansForums.net

leep82

-
Arms
Reaction score
131
Got a small job to do this week replacing an existing light fitting for a new customer. Im not familiar with the installation so dont know what sort of state it is going to be in. During my conversations with the customer they have asked for a certificate to be completed for the work. I told them that for such work i wouldnt normally issue a certificate as it falls under maintenance, but if that is what they're insisting on, and me
being keen to impress them, then i will go along with there wishes.

My question to you fellow sparks is how far you would go in regards to the testing and certification for such a small job. I have been told that i am unlikely to be able to gain access into the consumer unit other than to lock off the required circuit. With that in mind my plan was to take a Zs reading at fhe existing fitting prior to removal, so as to probe the means of an effective earth, and then once again when the new fitting is installed.

I was going to detail in the comments section my actions and results prior to removing the old fitting and then record my Zs value of the new fitting in the appropriate column. R1+R2 and IR readings i would detail as a limitation. Obviously i would record all other relevant info such as OCPD and type of earthing arrangement, but with regards to the testing have i done enough/not enough?
 
Minor works. You can do an R2 for dead continuity and also IR at the same time. Zs and any RCD testing if applicable.

Also cursory check of bonding and intake equipment, CU etc to ensure all is good.
 
Minor works. You can do an R2 for dead continuity and also IR at the same time. Zs and any RCD testing if applicable.

Also cursory check of bonding and intake equipment, CU etc to ensure all is good.
Would an IR test be practical though? I dont know what else is on the circuit and a small job suddenly becomes that little bigger if i have to start identifying why im getting odd readings.
 
Bit funny tho really, they want you to issue a certificate but they won’t let you test.
Its not that they wont let me test. I think its more about access into the distribution board, permits to work etc etc. I dont have a live working kit and have been told that the installation must remain on, so i can only isolate the circuit i am going to be working on.
 
Its not that they wont let me test. I think its more about access into the distribution board, permits to work etc etc. I dont have a live working kit and have been told that the installation must remain on, so i can only isolate the circuit i am going to be working on.


As I see it you can’t really do your dead tests at all. Just your zs and rcd.

You where quite right in your post that it doesn’t need a mwc but I’m not too sure about doing a half completed mwc.
 
If it’s connected to an rcd surely the ir test would give funny readings ?
I dont know what its connected to. The reason for the change is just to modernise an old dirty light fitting, which still works fine. Not due to a fault or anything.

As its currently working with no reported issues i didnt see the need to go down the route of performing R1+R2 and or IR test.
 
As I see it you can’t really do your dead tests at all. Just your zs and rcd.

You where quite right in your post that it doesn’t need a mwc but I’m not too sure about doing a half completed mwc.
I would just comment on the cert why all tests weren't performed. I think these people just want something as a record to say its been done and its ok.
 
We were told once by a scheme area engineer that as a minimum we should do a loop test if it was loads of fittings to put on spreadsheet readings at end of row etc.
 
1) R1+R2 or R2. 2) Insulation Resistance. 3) Polarity. 4) Zs. 5) RCD if applicable. I have an NICEIC 2392 learning guide, which suggests the essential tests are 3, 4 & 5 (5 if applicable) and if reasonably practicable 1 &2. BS7671 only refers to results of tests, as suggested in the model form App.6



From a thread a while back
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Oh and no LIM, it’s a Certificate, not a Report.
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Oh and no LIM, it’s a Certificate, not a Report.
Should i just leave blank the boxes for R1 and R2, IR tests?
 
1) R1+R2 or R2. 2) Insulation Resistance. 3) Polarity. 4) Zs. 5) RCD if applicable. I have an NICEIC 2392 learning guide, which suggests the essential tests are 3, 4 & 5 (5 if applicable) and if reasonably practicable 1 &2. BS7671 only refers to results of tests, as suggested in the model form App.6



From a thread a while back
Is that for an initial verification? Or a situation like im referring to?
 
I would do a loop test and RCD test if it's RCD protected. It's not really feasible to go further than that for a simple accessory replacement.
 
This is not an alteration to or extension of an existing circuit.
It’s replacement of an item of equipment.
As such most of the tests not relevant.
Yes, conduct a Zs test to confirm CPC continuity, that’s all that’s required.
Should i just leave blank the boxes for R1 and R2, IR tests?
Leave blank, draw a line through the part for the result or write N/A.
Drawing a line would probably be my choice, depending on how I feel.
If you leave it blank, it may be misconstrued that you have just forgotten to enter a value.
 

Reply to Like for like replacement and MWC in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Seeking advice, we have been replacing extractor fans for a local council and was originally told no ‘like for like’ replacement works needs a...
Replies
14
Views
914
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
893
Hi all. I have a small question about inspection interval labels. We all know to fit one of these labels with the relevant date upon completion of...
Replies
10
Views
833
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
755
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock