Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Would it not be ok if it satisfied the requirements of R< 50/Ia ? Where Ia is the max current of the protective device? So for 0.3 would be acceptable at 100A

any thoughts?
 
You have to use the current required to operate the 100A fuse 1200 @ 0.4s or 1800A @ 0.1s.
50/ 1200 = 0.04Ω

That's used for supplementary bonding and even there the actual conductor has to be <0.05Ω.

Main bonding conductor conductor must be <0.05Ω.
 
I think you are getting confused with your Ze measurements, what's the bonding conductor got to do with 100A main fuses?
 
My asking where he was testing to and from, as in his domestic situation it seemed as though he was using the 0,05 ohms as a guide for his expected reading of his bonding conductor, I didn't realise he was trying to determine the length of the bonding conductor.
I don't think he is.

In the original question he says

Does main bonding in every circumstance always need to be under 0.05. main bonding in a house where the main water was moved has 10mm cable but resistance of 0.25 ohms!!>>
I don't think the length has anything to do with it apart from the physical impossibilities.

 
That's the first time supplementary bonding has been mentioned, as I said where did he get his ohmic value for his main bonding from, where has he measured it to and from............................It's main bonding he has referred to in his question..... did he measure between two pipes, one end of a cable to another, a pipe to a cable I ask again where???
He's using the formula for whether (supplementary) bonding is required but using the wrong numbers.

See above post.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
762
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
858
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
416
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock