Discuss Main bondage in the UK Electrical Forum area at ElectriciansForums.net

So as Geoffsd and Serpico said:

for a 100A domestic supply, the Ia value would be either 1200 at 0.4s or 630 at 5s

To which the higher would make the maximum permittable resistance of the main bonding conductor is 0.041 ohms if R< 50/1200

The cable measured was directly from the conductor at the MET to the bonding clamp using croc clips?

So would a resistance of 0.25 Ohms mean that the bonding conductor is unsafe as the resistance is too high in the event of a fault?

Forget about resistance, select the right size job done. If the bonding conductor is in place and the right size, just test its resistance so that it relates to length and csa.
 
I think the point several people are trying to make here is that if it's a reasonable length of cable, correctly sized, then the reistance WILL NOT BE that high and there is an issue somewhere which needs looking into.
It may be 0.25 ohms now (still not acceptable), but what will it be in the future if the connection is poor or there is some form of corrosion at work?
 
from MET @ CU, (front of house) removed 10mm cable, then where the stopcock is for water (rear of extension of house) removed the 10mm cable there. The resistance of this between one end and the other is 0.25. ohms.

As i cannot see the run, nor is there easy access to where it may be, and the fact that there are 3 x 10mm cables at the MET I would like to think that it is one length of cable, but the resistance readings simply doesnt state that.

But the bonding continuity has been verified.
 
Is this not pretty simple?

the 0.25 ohms reading is not even in the ballpark of being vaguely acceptable for the multiple reasons given in this thread. Given that the incoming water pipe has been moved this would be a strong indication that when they moved it they jointed and extended the bonding cable to move the bonding point to the new incoming mains point, and the chances are that this joint is the cause of your high resistance reading for one reason or another.

If you were working for me I'd be seriously unimpressed right now tbh, stop dithering and get it sorted then move on to the next job, bonding of water and gas pipes is about as basic as it gets isn't it?

apologies if you're a trainee.
 
if the actual resistance value of the protective bonding conductors was of such great importance you'd think that IET electrical certificates of any format would require you to record these readings ?

but they dont........?
in fact they ask no more than to confirm connection with a simple tick box......
which for the most part can can be done visually and a poke around with a screwdriver.

one could then reasonably assume that by selecting the correct conductor size as per the relevent tables in bs7671 fulfils these obligations whether the actual resistance reading is 0.05 or 0.25 ohms.

just a thought........
 
Even to this inexperienced oik, if I got a reading as you are, my 2nd step would've been to get the wander lead out and check the cable end to end, then, seeing as I was under the sink, between MET and pipe ~ MET and clamp.
 
When I saw the thread title I too wondered what it was about and wondered if the Mods were up to no good having a laugh at us lol, I love these mis-printed threads, posted by a Iphone I bet lol.
 
from MET @ CU, (front of house) removed 10mm cable, then where the stopcock is for water (rear of extension of house) removed the 10mm cable there. The resistance of this between one end and the other is 0.25. ohms.

As i cannot see the run, nor is there easy access to where it may be, and the fact that there are 3 x 10mm cables at the MET I would like to think that it is one length of cable, but the resistance readings simply doesnt state that.

But the bonding continuity has been verified.

Hi Ultinator....bet you wish you'd not bothered with the test now and I bet you regret asking for advise on here......but you did and good on ya mate........10mm at 1.83 milli ohms per meter (measured end to end) suggests around 136m of 10mm cable (I know already stated)....now as this measurement was an end to end measurement then I'm sure you can see that there is something amiss here, unless of course the cable length is 136m long.......By the way I quite like Geoffsd touch voltage concept.....would love to hear anybody else's reasons why 0.05ohms is used as a recommendation...

And just out of interest, why is it every time I post, I have to copy it, because if it takes longer than say 2mins to post, I get logged out and lose what I've posted...confused? cos I'am
 
This is my take on it after a phone call to a much more knowledgeable friend.

The 0.05 value is BETWEEN simultaneously accessible extraneous parts, i.e. a gas pipe and a water pipe next to each other. Take for example this was the case, but each pipe was bonded separately back to the MET. Then the two would have to cross bonded.

The figure of 0.05 is not the value that needs to be achieved from the MET to the bonded extraneous part.
 

Reply to Main bondage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi I have a 1st fix domestic install on the go and need to leave a socket for other trades to use after me. There is no main bonding at the...
Replies
7
Views
840
I have a main panel beside my meter on the house built in 1987. Then a 4 wire feed into a 200 amp panel on an inside wall of my basement. All of...
Replies
1
Views
396
Not sure on this one. Mains water is coming up from the ground in lead pipe in bathroom. 2 inches of copper pipe before the stop tap. All...
Replies
4
Views
1K
Hello, my incoming supply has one main fuse that feeds the next door naghbour it leaves my house to go next door as shown in picture..it's the...
Replies
4
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock