Discuss Main bonding flow and return to oil boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

BLBelfast

-
Arms
Reaction score
36
Hi this is pickling my head and any advice is appreciated. I have a TNCS system. I have an external oil boiler fed from the house in a detached garage. The main water in the house and the flow and return from the boiler are all bonded back to the house MET from within 600mm of where they enter the house.

Do they need bonded where they enter the garage aswell from the garage CU which will be a TT system due to extraneous conductive parts being present...IE water supply from house? The garage is around 3m from the house
 
In my opinion it would be better to take a suitable bonding conductor to the outbuilding and have the outbuilding connected to the TNCS earth. This is assuming the heating flow and return are continuous metal pipes and so bonding them in the outbuilding will be effectively connecting it to the TNCS earth anyway.

I'm also wondering whether these pipes, if metal, could be used as the bonding conductor?
 
In my opinion it would be better to take a suitable bonding conductor to the outbuilding and have the outbuilding connected to the TNCS earth. This is assuming the heating flow and return are continuous metal pipes and so bonding them in the outbuilding will be effectively connecting it to the TNCS earth anyway.

I'm also wondering whether these pipes, if metal, could be used as the bonding conductor?
I thought pipes are not allowed to be used for bonding conductors according to the regulations in the 17th edition.
 
I thought pipes are not allowed to be used for bonding conductors according to the regulations in the 17th edition.
not sure. they're not allowed as earthing conductors. agree with dave, pipes will connect the outbuilding to the TNCS anyway, so add a decent rod as well. pre-empt the 18th.
 
Oil Pipes and gas pipes can't be used as protective conductors regulation 543.2.3 I think it is, not sure about bonding conductors without looking it up
 
No worries, though I am inclined to ask the same question again. Metal pipes can be used as a means of earthing if they are suitable (permission of the owner, size, reliability etc etc)
agreed. it's public service pipes that can't be used as they are liable to be replaced in plastic.
 
Thanks for the advice. Embarrassing as this is as its a recent purchase i just realised its a TNS system. I dont know why I presumed it was TNCS :-(

My thinking now is simply leave the 10mm main bonding from the house MET to the flow and return entering the house. Export the TNS earth to garage, Likely a 6mm 3 core swa and bond from the garage CU to the pipes entering the garage again in 6mm. The oil line wont be touched. Does this sound reasonable? Do i even need to bond entering the garage as they are already connected to the TNS in the house which is a few feet away. They are also strung across on a bit of timber so they dont touch the ground.

It might seem daft to ask confirmation but I dont normally deal with domestic and its just its my own house or I wouldn't be doing it.

Any advice appreciated thanks
 
The oil pipe would normally need to have a main bond too.

As it stands I don't see that the flow and return pipes would need additional bonding if one earthing system is in use, Especially considering that they are installed above ground
 
And if the flow and return have their own main bond back to the MET as stated [Which is unusual] I'd be inclined to just cross bond from them to the oil feed near the boiler in 10mm.
 
And if the flow and return have their own main bond back to the MET as stated [Which is unusual] I'd be inclined to just cross bond from them to the oil feed near the boiler in 10mm.

Not unusual in this situation where they are strictly speaking extraneous parts entering the installation.

I think to take the regulations absolutely literally they should be bonded as extraneous parts entering the outbuilding too, but since those very pipes can probably be used as a bonding conductor anyway it's fair to accept them as they they are.
 
Yeah the 10mm main bonding to the flow and return is definitely there as i wired it myself.

Thanks for taking the time and giving your advice. And i will bond to the incoming oil line in 10mm from the garage cu then though it also doesnt come into contact with the ground so not sure what the theory of this is. It's literally a 2m pipe from tank to boiler.
 
Yeah the 10mm main bonding to the flow and return is definitely there as i wired it myself.

Thanks for taking the time and giving your advice. And i will bond to the incoming oil line in 10mm from the garage cu then though it also doesnt come into contact with the ground so not sure what the theory of this is. It's literally a 2m pipe from tank to boiler.


The most popular theory at the moment is to test it to establish whether or not is extraneous to establish whether or not main bonding is required.
Personally I interpret ten regulations slightly differently, but I'm in the minority with that opinion and am probably wrong.
 
No worries, though I am inclined to ask the same question again. Metal pipes can be used as a means of earthing if they are suitable (permission of the owner, size, reliability etc etc)
Hi - just reading through 542.2.6 and it seems a gas or flammable liquid pipe should not be used as an earth electrode, but I may have misunderstood (?).
 

Reply to Main bonding flow and return to oil boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
655
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
463
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
952
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock