Discuss Mains Riser to a top flat ? in the Australia area at ElectriciansForums.net

E

Electroreaper

Hi Guys

Just looking for some advice on how to run a mains riser?

Its a Victorian Terraced House and the top of the house is the 3rd floor as it is to be renivated into a flat.

The Meter and fuse boards for the other floors are in the ground floor kitchen.

I plan to run a mains riser 25mm to a split board inside the top flat.

just how to i get the cable up there?

some of the exsisting cable for the other floors goes up the stairs! round the staircase.

do i go armoured and run the cable on the outside of the building but need scaffolding or try and somehow run it up through each floor?
 
Run armoured on the outside mate, inside sounds like a nightmare. I wired up a load of council flats like this, only first floor flats though
 
Distributors run hybrid up the side of buildings and it is not armoured and often protected by 400A substation fuse, so I would not have any hesitation in running SWA outside, (done it before and will do it again)
 
Thanks yeah it would be a straight run with the SWA but the building is so tall i would need scafolding and there is a conservetory on the back of the kitchen with a glass roof!
 

Reply to Mains Riser to a top flat ? in the Australia area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
810
Hi Guys, We are undertaking a large development and just want to get some ideas on how others would supply each unit. There will be a rising...
Replies
7
Views
2K
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
640
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
289

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock