andybenw

Hi,

I have had 3 phase cut-out and meters for 3 flats moved from my cellar to outside meter cabinet. Sparky has installed switch fuses and around 15 metres of SWA for each flat to relink to old supply point. Work looks decent so I am not disparaging said sparks work. I have a query though.

He is describing this as minor works as no new circuits have been added. Is this correct?

Cheers in advance, Andy.
 
New cable, new switch fuses, new routes, new origin position.... yep, 3 new distribution circuits. A minor works cert will not be sufficient, an installation cert is what is required and notification to LABC.
 
Last edited:
I did suspect that Andy. I assume he should notify the work and issue me with an EIC with the caveat "new installation of switch fuses and cable only, Periodic Inspection recommended"

I should add the flats are not anywhere near 17th edition with 1970's 3036 fuseboards.
 
I have, but by cheque which I could stop if need be.
I strongly suggest you do not do that, the work has been done and to a standard of your satisfaction, why don't you speak to him face to face like a man and not a coward who goes on forums suggesting things like stopping his cheque because someone you have never met suggested it. The guy has a family I suspect and yet you want to stop his cheque even though your happy with the work due to a certificate, talk to him and resolve it the dignified way for god sake geez.
 
Last edited by a moderator:
No problem Murdoch. I agree it is perhaps open to interpretation hence me asking the question. He is a member of Elecsa and able to notify. He has promised me a minor works certificate. If the balance of opinion on here is for notification I shall query him about it.
 
I would point out that notification and type of certificate are not related.

Even if considered not notifiable you should still get an Electrical Installation Certificate and Schedules of Inspection and Test Results.
 
I strongly suggest you do not do that, the work has been done and to a standard of your satisfaction, why don't you speak to him face to face like a man and not a coward who goes on forums suggesting things like stopping his cheque because someone you have never met suggested it, I don't like people like you, faceless slimy little person. The guy has a family I suspect and yet you want to stop his cheque even though your happy with the work due to a certificate, talk to him and resolve it the dignified way for god sake geez.

MDJ. Very abusive. I am simply gathering information prior to speaking to the man. As present I have not been issued with any certification. I had to raise the issue with him just prior to him leaving, and it was only then that he promised to send me a minor works certificate.

Do you not agree that I should arm myself with information prior to contacting him?
 
I would point out that notification and type of certificate are not related.

Even if considered not notifiable you should still get an Electrical Installation Certificate and Schedules of Inspection and Test Results.

Thanks for the answer Geoff. So you are on the side of EIC and not minor works?
 
MDJ. Very abusive. I am simply gathering information prior to speaking to the man. As present I have not been issued with any certification. I had to raise the issue with him just prior to him leaving, and it was only then that he promised to send me a minor works certificate.

Do you not agree that I should arm myself with information prior to contacting him?
I agree you need to talk to your spark about issuing the correct certification, coming on a forum talking about stopping cheques even though you are happy with the standard of work is what got my goat up, apologies for the soapbox bit, I have calmed now, just have a chat to him in a friendly manner, say you insist on a Electrical Installation Certificate and I would think he will come around to your demands as the customer, regarding the Minor works,I must admit he sounds a bit of a ---, but if the work is good then the only concern is certification and stopping payment isn't the right way forward IMO.
 
I agree you need to talk to your spark about issuing the correct certification, coming on a forum talking about stopping cheques even though you are happy with the standard of work is what got my goat up, apologies for the soapbox bit, I have calmed now, just have a chat to him in a friendly manner, say you insist on a Electrical Installation Certificate and I would think he will come around to your demands as the customer, regarding the Minor works,I must admit he sounds a bit of a ---, but if the work is good then the only concern is certification and stopping payment isn't the right way forward IMO.

I appreciate your answer. To be honest I am not particularly bothered about certification as I am happy the work is safe. But one of the other flats is selling and could get caught out with wrong certificate. I assume by your answer you also think a EIC is required as opposed to a minor works.
 
I appreciate your answer. To be honest I am not particularly bothered about certification as I am happy the work is safe. But one of the other flats is selling and could get caught out with wrong certificate. I assume by your answer you also think a EIC is required as opposed to a minor works.
Yes I would agree you require a EIC especially as you intend to sell, you need to have a chat with him, if you get any issues about it then come back and we can advise the next step, but talking is the answer.
 
I have recieved a quick reply from him. He has quoted the regs and stated he should issue a minor works. As Murdoch says it does seem it is a bit of a grey area. He will be issuing 3 seperate certificates, 1 for each flat.

I am happy to accept this as I feel as he is approachable, registered with Elecsa and I think if anyone queries in future(eg during a sale) I will be able to show his e-mail reply as an answer.

Am I right in thinking that whilst its a grey area for EIC/minor works (some views will obviously differ), the work is definitely not notifiable?
 
I have recieved a quick reply from him. He has quoted the regs and stated he should issue a minor works. As Murdoch says it does seem it is a bit of a grey area. He will be issuing 3 seperate certificates, 1 for each flat.

I am happy to accept this as I feel as he is approachable, registered with Elecsa and I think if anyone queries in future(eg during a sale) I will be able to show his e-mail reply as an answer.

Am I right in thinking that whilst its a grey area for EIC/minor works (some views will obviously differ), the work is definitely not notifiable?
How??.
 
From BS7671

page 394 notes for minor electrical works certificate

the minor works certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of a new circuit.

page 31 Part 2: definitions

Minor works. additions and alterations to an installation that do not extend to the provision of a new circuit.


He has without doubt provided 3 new distribution circuits and an EIC is the appropriate cert.
 
From BS7671

page 394 notes for minor electrical works certificate

the minor works certificate is intended to be used for additions and alterations to an installation that do not extend to the provision of a new circuit.

page 31 Part 2: definitions

Minor works. additions and alterations to an installation that do not extend to the provision of a new circuit.


He has without doubt provided 3 new distribution circuits and an EIC is the appropriate cert.

Hum. The circuits are replacing old ones!
 
Hum. The circuits are replacing old ones!

But the route is not the same, and I have no idea if the cable type, size, and OCPD type and size is the same, but would guess they are not. The OP could confirm this.

If it were a like for like swap of cable I would agree with you, but a new origin, a new OCPD, a new route, and a new cable makes a new circuit for me.
 
But the route is not the same, and I have no idea if the cable type, size, and OCPD type and size is the same, but would guess they are not. The OP could confirm this.

If it were a like for like swap of cable I would agree with you, but a new origin, a new OCPD, a new route, and a new cable makes a new circuit for me.

And this is my point really, we have half information, at best, from a non competent person.......
 
Based on the info provided up to now, if it were my job, I would have regarded them as new circuits and issued EIC.

If this guy's Elecsa registered spark is happy to issue a MWC and the customer is happy then who am I to interfere with happiness ? lol
 
Based on the info provided up to now, if it were my job, I would have regarded them as new circuits and issued EIC.

If this guy's Elecsa registered spark is happy to issue a MWC and the customer is happy then who am I to interfere with happiness ? lol

I would also have done an eic or 3 for what it's worth!
 
And this is my point really, we have half information, at best, from a non competent person.......

Sorry,I'll try and provide a bit more info.

Cutout before move 3x 100A fuses. 1 flat tailed straight out, with the other two sub mained via 60A fuse switches and 16mm T+E.

Situation now. New cutout with 3x 100A fuses. Tailed to 3x 80 switchfuses. Linked back to original position with 16mm SWA. All 3 circuits now with 60A switchfuses in cellar as being used to gland SWA and there was a spare from previous Economy 7. Also a seperate 16mm earth wire linking previous MET to new. I'm not an electrician, but have passed C&G 2382 and the new C&G 2394 as part of leaving forces so not completely non competent, although if I was a practising electrician I admit I would fall into the bracket of Electrical Trainee.

I have been thinking (dangerous) and either he has set up a new distribution board within the new meter cabinet(EIC) or simply extended the current supplies to each flats Consumer units(3x minor works). Grey area even with the rule book?
 

Reply to Major or Minor Works? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I’m brand new to the site and hope everyone is doing well. My question is this: I have a 2365 level 2 diploma and have been doing...
Replies
6
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K
Hi, Really appreciate the help in advance.. I’ve been asked to install an outside socket and a floodlight with PIR. I’m a 4th year apprentice...
Replies
9
Views
2K
Hi, I’d appreciate views on the fuse board. https://ibb.co/xj0BtZt It’s been completely rewired and I’m unhappy with the quality. I’ve...
Replies
149
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock