P

pprendeville

Just want to find out if this overload unit will be able to be set for the max rated current on this motor. I don't think it will though as it can only be set to 1.6A and the max rated current is 2.1A in delta? Am I right in saying this?
 

Attachments

  • maximum rated current demand of the motor and overload unit.jpg
    69.4 KB · Views: 29
The full load amps for your motor is 1.2 amps at 380v so if you are running at 380-415v and 3p star connected then the o/l is adequate.
The o/l would only be overloaded if you were running the motor at 220v with 3p delta connections.
 
is it 3phase?
your motor faceplate has 220v @ 2.1a or 380v @ 1.6a

yes it's 3-phase.

The full load amps for your motor is 1.2 amps at 380v so if you are running at 380-415v and 3p star connected then the o/l is adequate.
The o/l would only be overloaded if you were running the motor at 220v with 3p delta connections.

How come the full load current (star config 380V) is less than the delta current (220V). I thought ohms law stated that the higher the voltage the higher the current. I=V/R etc. Is the resistance of the windings greater while in star? Prob dumb questions for you guys but I'm just starting out. Appreciate the help.
 
Last edited by a moderator:
The higher the voltage the lower the current.

Easiest way to demonstrate is a transformer (i.e. welder) 38volts out at 100 amps would require a current of 16.5 amps at 230v in. ignoring efficiency.

Someone else will probably explain the formula. I forgot all that stuff over forty years ago.
 
The higher the voltage the lower the current.

Easiest way to demonstrate is a transformer (i.e. welder) 38volts out at 100 amps would require a current of 16.5 amps at 230v in. ignoring efficiency.

Someone else will probably explain the formula. I forgot all that stuff over forty years ago.

Ah no, I was being a bit thick. Sure if the number above the line increases then I will have to be smaller. Doh. Could also use the gear train to illustrate your point. Thanks for the help.
 

Attachments

  • Geartrain.jpg
    49.9 KB · Views: 19
I should perhaps add that motor windings in modern low Kw. motors are typically wound to facilitate use in countries such as the US where 220 per phase is the norm. Larger motors use star delta in a different way to enable a soft start through a star connection with a timed switch overto delta when the motor reaches its rated speed. Both connections at 380/415v. This method is easier on larger motors than a straight DOL start in delta and draws less current .
 

Reply to Max rated current demand of the motor and overload unit in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
I have been asked/invited to "post more", lol, so let me make another post right away. I thought of sth worthy to post, of interest to many, I...
Replies
2
Views
520
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
530
Hello Can anyone confirm for me what the following spec for a Wago TopJob 2202-1201 din rail connector means? The connector can accept max 4mm...
Replies
4
Views
1K
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
690

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock