Discuss MCB kA Rating 3 phase Board? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

P

Piratepete

Hi Guys

I don't do much 3 phase but am used to seeing them populated by 10kA MCBs.

I'm dealing with a board which has a mixture of 6 and 10 kA 3 phase and 1 phase MCbs.

Z line measures 0.13 Ohms and Isc line is 1.6 kA. The supply fuses are 200 Amp.

So 6 kA MCbs are ok in this situation then?

Pete :yes:
 
Hi Guys

I don't do much 3 phase but am used to seeing them populated by 10kA MCBs.

I'm dealing with a board which has a mixture of 6 and 10 kA 3 phase and 1 phase MCbs.

Z line measures 0.13 Ohms and Isc line is 1.6 kA. The supply fuses are 200 Amp.

So 6 kA MCbs are ok in this situation then?

Pete :yes:


Do you mean Zs is 0.13 and PSC is 1.6 KA ?
 
What exactly have you measured here? The OP suggests you've measured the L - L loop impedance and short circuit current, but your reply to Pete suggests that you've measured the earth loop impedance?
Make your mind up!


Sent from my iPad using Tapatalk
 
What exactly have you measured here? The OP suggests you've measured the L - L loop impedance and short circuit current, but your reply to Pete suggests that you've measured the earth loop impedance?
Make your mind up!
Sent from my iPad using Tapatalk

Whatever. It doesn't help that the installation test sheets refer to Ze at a consumer unit as Zs. So excuse my ambiguity. My meter was connected to Line, Neutral and Earth. I tested each phase for worse case. I understand that if I take the single phase value and double it, this gives me worst case scenario.
Pete
 
Last edited by a moderator:
Whatever. It doesn't help that the installation test sheets refer to Ze at a consumer unit as Zs. So excuse my ambiguity. My meter was connected to Line, Neutral and Earth. I tested each phase for worse case. I understand that if I take the single phase value and double it, this gives me worst case scenario.
Pete

Where is the board fed from?
 
My meter was connected to Line, Neutral and Earth.

So you didn't do any tests from one line to another line? Which is how I would interpret 'Z line'. If the resistance of all the conductors is equal, then the PSCC for a line-line fault will be approx sqrt(3) x that for a line-neutral fault. However there can be situations (e.g. with a reduced-neutral cable) where it is higher by a greater factor than the ratio of the voltages. I always do the L-L tests rather than assume.
 
So you didn't do any tests from one line to another line? Which is how I would interpret 'Z line'. If the resistance of all the conductors is equal, then the PSCC for a line-line fault will be approx sqrt(3) x that for a line-neutral fault. However there can be situations (e.g. with a reduced-neutral cable) where it is higher by a greater factor than the ratio of the voltages. I always do the L-L tests rather than assume.
I do as well but the problem is not all MFT's can do L-L tests.
 
So you didn't do any tests from one line to another line? Which is how I would interpret 'Z line'. If the resistance of all the conductors is equal, then the PSCC for a line-line fault will be approx sqrt(3) x that for a line-neutral fault. However there can be situations (e.g. with a reduced-neutral cable) where it is higher by a greater factor than the ratio of the voltages. I always do the L-L tests rather than assume.

The DB is right beside the DNO's meter and 200 Amp cutouts and the Neutral Line is huge as is the Earth. The Neutral is the same size as the phase cables. Can't tell you what as I've never installed this size.
Pete
 
I do as well but the problem is not all MFT's can do L-L tests.

Ah, good point, didn't think about that because we've only ever had ones that do 400V tests because most of the stuff we work on is 3-phase. In this case it sounds like the resistances will be the same and the MCBs well in for Icn
 
Assuming same size neutral cable as lines cables... my understanding was that a line-line fault current would be sqrt(3) times the L-N PSCC; but a symmetrical fault would be 2 times the L-N PSCC. However I've never seen a convincing set of maths to verify this. There are hints of it in this link... but "Z" is ill-defined there, and there seems to be a factor of 2 out.

Question: would a single phase circuit breaker in a 3-phase board ever have to deal with a symmetric fault? A 3-phase breaker, sure (perhaps a broken star-delta starter?). Because I've seen situations where sqrt(3) x PSCC is on the "ok" side of the line, whereas 2 x PSCC is more on the "explody fireball of doom" side...
 
Whatever. It doesn't help that the installation test sheets refer to Ze at a consumer unit as Zs. So excuse my ambiguity. My meter was connected to Line, Neutral and Earth. I tested each phase for worse case. I understand that if I take the single phase value and double it, this gives me worst case scenario.
Pete

It's not whatever, it's an important technical detail. This is a technical trade and anyone practicing it should be capable of using a reasonable degree of technical accuracy in their communication.

It's no good just saying that your meter was connected to three points, especially when you should be carrying out a test which only needs two test leads, so that in itself suggests that you have carried out a three wire low current test instead of a high current test so your results are quite possible wrong as a result of this.
So what were you measuring? L-E or L-N?

There is no such thing as Ze at a consumer unit, Ze is a measurement of the external loop and is only at the supply terminals, before the consumer unit.





Sent from my iPad using Tapatalk
 

Reply to MCB kA Rating 3 phase Board? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Need to source Type B 3-phase distribution & 3P MCBs for EVSE, 1P RCBOs etc. so my sparky can install. A 6-way 3P board will suffice. Wondering...
Replies
23
Views
3K
Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock