  • new build house 3 years old

  • Cold water supply comes into the house at the kitchen

When turning the mixer tap on in the kitchen it sometimes trips the water pump, it does not trip the pump from any other point in the house either mixer or single tap.

I have changed the pressure reducing valve, renewed the mixer tap and fitted a non return valve on the hot outlet under the kitchen sink and replaced the 6a MCB.

Any help advice greatly appreciated.
 
It's a Grundfos shower pump STN3.0
Hi - reading the manufacturer's instructions it says to be connected via a fused connection unit with a 5A fuse (me - this would normally be a spur off a power circuit with its own 16A to 32A mcb) What's the story with using 6A mcb?
 
Buck Taylor RE # 1: Before you modify the electrical supply to the pump you should confirm first that the Grundfos pump is plumbed correctly. For starter, it must not be plumbed directly off the cold water mains - it must have a feed from a cold water storage tank located above the pump.

See Section 3 Installation of:

Grundfos https://showerpumpselector.co.uk/pdfs/installation-advice.pdf
 
Buck Taylor RE # 1: Before you modify the electrical supply to the pump you should confirm first that the Grundfos pump is plumbed correctly. For starter, it must not be plumbed directly off the cold water mains - it must have a feed from a cold water storage tank located above the pump.

See Section 3 Installation of:

Grundfos https://showerpumpselector.co.uk/pdfs/installation-advice.pdf
Hi, thanks- yeah their is a cold water tank in the loft space. I have replaced the 6 amp type B With a 6amp type C MCB and it is still tripping?
 
you could always advise the customer to bath in the Clyde.:D:D:D.
 
I need some more information please:

a. What does it say on the pump rating plate for running current and for power?

b. What is the size and installation method of the cable feed to the motor from the CU?

The manufacturer states a 5A fused spur and thus BS1361 fuse protects the pump. I suspect - from some quick comparison calculations between a 5A BS1361 and a type C 6A mcb - that the product of the pump motor's short (less than 1s) start time and square of the high starting current(5-10 In) exceeds the no-trip Isquaredt of the 6A mcb by some margin but not the pre-arcing Isquaredt for the 5A BS1361 fuse (which is 44A2s). And that the fuse provides some current limiting which helps matters.

What I would do is a quick experiment: at the CU see what happens if you swap the 6a mcb for a 5A HRC or a BS1361 fuse and whether then the pump starts without problems.
 
Last edited:
Hi, thanks- yeah their is a cold water tank in the loft space. I have replaced the 6 amp type B With a 6amp type C MCB and it is still tripping?
Hi - why is it on a 6A MCB ? Commonly they would be on circuit with at least 16A MCB, via a 5A fuse as per @marconi.
Then if it blows the manufacturer specified 5A fuse we are headed in a certain direction ...
 

Reply to MCB tripping intermittently in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Calling all electrical professionals / boiler tradesmen -WE NEED YOUR HELP! Every so often (twice in the last two days) when running the hot...
Replies
15
Views
430
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock