It’s a 50m run on basket
I have on my drawing a 27kw 3-phase +N isolator
That is all it’s max travel through celotex is 3m
I have looked into it before I posted
Something along the lines of this
Amps=27kw divided (square root 3 x pf (1.0) x volts (400v) )
I get around 89a which doesn’t sound right to me On 3 phase unless I’m missing something
Also looked online and it’s come out on a calculator
39a per phase so a 40/45a 3phase Mcb would be suitable
Am I wrong here at all ?
Thanks
There isn’t enough information to be able to do the calculations.
Without knowing what the load is it is not really possible to establish whether an mcb is suitable or if fuses/mccb protection is required.