Discuss Need Help with Breaker Sizing 3 phase in the The Welcome Forum area at ElectriciansForums.net

Reaction score
0
Good day to all. Please correct me if im wrong and also want your professional inputs.
I am servicing a pump motor rated at 415vac 3 phase 11kw power. The breaker is at 20amperes. The complain is everytime the motor automatically stop when the tank is full the breaker always trip during the motor's initial run. When i checked the start up current the reading is around 40amperes. But during nkrmal run the reading is only 20 amperes.
So is it because the starting current is high that is why the breaker trip?
Now i changed the breaker with 32 ampere rating and see what happens.
Your advice is highly appreciated.
Thanks
 
Good day to all. Please correct me if im wrong and also want your professional inputs.
I am servicing a pump motor rated at 415vac 3 phase 11kw power. The breaker is at 20amperes. The complain is everytime the motor automatically stop when the tank is full the breaker always trip during the motor's initial run. When i checked the start up current the reading is around 40amperes. But during nkrmal run the reading is only 20 amperes.
So is it because the starting current is high that is why the breaker trip?
Now i changed the breaker with 32 ampere rating and see what happens.
Your advice is highly appreciated.
Thanks
What type of CB is it B,C,D, etc?
 
20180420_100930.jpg
 
That is a thermal motor circuit breaker. Is this a recent installation or has it been operating okay in the past.
 
Yeah a recent installation from the other person just endorsed to me. Now i am the one handling this and their common complain is frequent trip of this breaker after every automatic shutoff from the level sensor of water tank.
This is the breaker going to soft starting relay then going to 11kw 415v 3 phase pump motor
 
Yeah a recent installation from the other person just endorsed to me. Now i am the one handling this and their common complain is frequent trip of this breaker after every automatic shutoff from the level sensor of water tank.
This is the breaker going to soft starting relay then going to 11kw 415v 3 phase pump motor
Have you spoken to Schneider technical for advice?
 
That is a motor overcurrent protective device, it is designed to be set to the flc of the motor if DOL, as it starts at 24 I can hazzard a guess for an 11kw motor this will be about the setting, the motor plate will tell you what rating it should be set to, the soft start should limit inrush.
What is the duty of the motor?, what is the duty allowance of the soft start?, is that the device tripping in the picture?

Turning this overload up is not the way to resolve this, you need to know what is causing the tripping and why, if it is a poor design or a fault then increasing the overload setting may cause bigger problems and could damage the motor and any risks associated with that.

My final question and may change how we reply to your posts is -

What is your electrical background, experience and qualifications ?... my concern is with not recognising a motor overload trip and another thread asking about CCC of a cable it thus raises concerns about the work you are doing here.
 
Honestly my background is electronics with some experience in electricals but no formal electrical study. I am assigned on plc controlled machines but since our electrical guy resigned and my boss is cutting expenses by hiring another person she want me to take over electrical job.
Maybe you can give me some helpful sites that i can read.
Because what we have is a motor pump to transfer water to other tanks.
 
Fully appreciate your honesty in your position and you have my sympathies if that is the position you have been put in, I must add that the forum has to be seen to give both safe and correct advice for members relative to the experience, training and position they hold, it is clear you are undertaking work out of your field through no fault of your own and unfortunately we do not allow step by step guides especially in this sector of the industry.
I cannot advice of any other forum that would be willing to advice you as we all tend to follow similar rules, I think you need to be honest with your boss but given your origin I can understand if this is not an option but as I have stated before, we have safe advice as a priority and that would be in your case to get a competent person in, may I stress this is no dig at your competence in your own field, it seems you are obviously been asked to undertake work that is out of your training and experience so with all respect to your position I am only left with the option to close the threads you posted.
 

Reply to Need Help with Breaker Sizing 3 phase in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
638
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
667
Hey guys, what does for example 300A rating on a 3 pole MCB means? Does it mean each phase carries 300A i.e. (Current in R=300A, Y=300A, B=300A)...
Replies
8
Views
2K
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock