The protective devices are listed as 60898 when in fact they are 61009.
 
How old is that Certificate as the schedule of test results doesn't seem to reflect all the inclusions suggested by the current version of BS7671.
 
Some of the test results look a bit made up, e.g. the Zs values for the radials - but made up by someone who doesn't know what they should look like. I also find Fusebox RCBOs all tend to have somewhat slower trip times than the results, but maybe your electrician had a particularly good batch!
 
Some of the test results look a bit made up, e.g. the Zs values for the radials - but made up by someone who doesn't know what they should look like. I also find Fusebox RCBOs all tend to have somewhat slower trip times than the results, but maybe your electrician had a particularly good batch!
Ze is apparently 0.61 but the Zs readings seem wrong when comparing to R1+R2.
 
As the certificate is a complete counterfeit I don't expect the content to be of any worth. As long as the job itself looks safe I'll move forward.
 
As the certificate is a complete counterfeit I don't expect the content to be of any worth. As long as the job itself looks safe I'll move forward.
When was it done.
 
Who do those cheap tools belong to in pic four as they have disappeared in the pic with the consumer unit cover in place.
 
As the certificate is a complete counterfeit I don't expect the content to be of any worth. As long as the job itself looks safe I'll move forward.
Even if the job looks safe, if the circuits were not actually tested, then they could be potentially dangerous. For example, unearthed metal class I light fittings, sockets with polarity errors or no earth, etc. You only find these things out when the testing is done properly.
 
  • Like
Reactions: DPG
a week last Thursday - 9 days ago
Well that Certificate is not in line with the current version of BS7671 and whilst you don't have to follow this standard word for word I would expect the NICEIC to. So are you going to fill us in with the full story as in #1.
 

Reply to New CU Installation (is it a good job)? in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top