Discuss New electric cooker causing power to trip at fuse. The fuse is reluctant to flick back on after. in the UK Electrical Forum area at ElectriciansForums.net

I'm assuming the cooker cable comes from the ceiling down to this, has it now moved to the left or right, with this junction box and cable plastered and tiled over?

Ok so your right the cable came from the ceiling... it used to be directly connected to the isolation switch at this location.

In order to move the isolation switches nearer to the Cooker and from the middle of the wall we needed to extend the wiring that's where my father in law contacted a electrician whom said this would be fine. The junction box was used at the location and then left buried in the wall.

Yes it is plastered over.... not tiled.

The cooker wire comes from this location to the isolation sockets.

This then goes to a junction box (cooker one) then from that to the oven
Ok so your right the cable came from the ceiling... it used to be directly connected to the isolation switch at this location.

In order to move the isolation switches nearer to the Cooker and from the middle of the wall we needed to extend the wiring that's where my father in law contacted a electrician whom said this would be fine. The junction box was used at the location and then left buried in the wall.

Yes it is plastered over.... not tiled.

The cooker wire comes from this location to the isolation sockets.

This then goes to a junction box (cooker one) then from that to the oven
When say cooker junction box it's a 1 gang 45 amp box fixed to the wall behind the cooker
 
Hi - I think its likely your recent works are the cause. The joint(s) or the oven itself. Any Certificate from the new Consumer Unit job? I agree with earlier advice, I think you need a friendly Electrician to help you now :) .
 
We've all seen this done before, I think, but it dont make it correct, not just for the reasons already mentioned.

It's one of those things that could be fine and last years but now the OP has a fault these are the things you really wish you hadn't done.

It can be proved that this junction is not the cause of the fault, if that's the case, but it will never be correct and it will always be a potential hazard.
Thanks for your advice.

I appreciate your time to help.

Thank you
 
Hi - I think its likely your recent works are the cause. The joint(s) or the oven itself. Any Certificate from the new Consumer Unit job? I agree with earlier advice, I think you need a friendly Electrician to help you now :) .
Yes there is a certificate I believe.

What's best way to find a reputable electrician.

What the likely cost of an investigative visit.

My priority now is to get it tested and checked

Thanks
 
look for a local guy who has been around a long time. Small guys rely on reputation and if they are long established it is normally a good sign. NICEIC or other schemes are no longer a guarantee of quality. An hours labour should be sufficient to find (but not necessarily rectify) the cause.
 
Ok so your right the cable came from the ceiling... it used to be directly connected to the isolation switch at this location.

In order to move the isolation switches nearer to the Cooker and from the middle of the wall we needed to extend the wiring that's where my father in law contacted a electrician whom said this would be fine. The junction box was used at the location and then left buried in the wall.

Yes it is plastered over.... not tiled.

The cooker wire comes from this location to the isolation sockets.

This then goes to a junction box (cooker one) then from that to the oven

When say cooker junction box it's a 1 gang 45 amp box fixed to the wall behind the cooker
I wouldn't get your father in law to do more electrical works for you (harsh but true). Also wouldn't get the electrician he contacted who said this would be ok, I'd be getting another electrician out to look at it.
 
Well I thank you all for your help and comments

more than likely the fault will be due to a fault due to a damp element when I think of it sitting unused for a while

I understand the wiring and works were not done to a standard you all deem acceptable and I will have to save to afford a qualified electrician to test and resolve.

Next steps
  • Work overtime
  • Get an electrician to test the wiring
  • Hopefully find the fault
  • Fix it
  • Never attempt to sort the kitchen on a budget again.
I am curious would I ever now be able to obtain a certificate of safety with this buried JB?
 
Well I thank you all for your help and comments

more than likely the fault will be due to a fault due to a damp element when I think of it sitting unused for a while

I understand the wiring and works were not done to a standard you all deem acceptable and I will have to save to afford a qualified electrician to test and resolve.

Next steps
  • Work overtime
  • Get an electrician to test the wiring
  • Hopefully find the fault
  • Fix it
  • Never attempt to sort the kitchen on a budget again.
I am curious would I ever now be able to obtain a certificate of safety with this buried JB?
Not being funny but no spark in their right mind would ever issue an Electrical installation Certificate or even a minor works certificate for work they haven’t done or at least witnessed every stage of. Anyone who says that they will should really be avoided like the plague. The best you may get is an EICR. (Electrical Installation Condition Report) I’m not familiar with the PART P side of things as I’m not in England or Wales but I don’t think that an EICR would be enough to certify that it complies without additional charges at the very least.
 
Is it just me or is the edge of that double socket sitting on top of the 45A DP Switch?
quite common with the new metal accessories as they are just that bit wider than older plastic ones so if the back boxes are too close they over lap. i suspect the cause is that they have used dual backboxes so the socket and middle fcu are in same one, not enough space in middle for them, hence the over lap.
 
As I said earlier in the thread... if you want to get it regularised by building control, you'll need to have a chat with them and find out who they'll accept an EICR from.

Once you know who they'll accept it from, you can engage someone and have them do the EICR and then submit it to BC.

I've done one, cost the lady over £300 I think in building control fees, plus my time and materials (in her case 3 days of testing and remedial work).
 
With those AEG ovens they use hex screws and unless you crimp the cable ends you have to split it around the screw. its very easy to get a loose strand that is sticking out touching the oven body. which is at earth potential and then trip the rcd. I have had it happen, turn oven on fine, adjust menus etc... then once it starts heating up and pulling a high current it tripped out. When I went to have a look it was a a single strand I had missed that was poking out underneath rest of the cable. been very attentive with them since and crimping again.
 
With those AEG ovens they use hex screws and unless you crimp the cable ends you have to split it around the screw. its very easy to get a loose strand that is sticking out touching the oven body. which is at earth potential and then trip the rcd. I have had it happen, turn oven on fine, adjust menus etc... then once it starts heating up and pulling a high current it tripped out. When I went to have a look it was a a single strand I had missed that was poking out underneath rest of the cable. been very attentive with them since and crimping again.
This could well be it you know. I remember it was tough and we made a few attempts with the wiring to split it around the screw neatly.

I will check that.

Thanks Gavin
 
quite common with the new metal accessories as they are just that bit wider than older plastic ones so if the back boxes are too close they over lap. i suspect the cause is that they have used dual backboxes so the socket and middle fcu are in same one, not enough space in middle for them, hence the over lap.
OP has already said that is was patresses used and an error on there part.
 
This could well be it you know. I remember it was tough and we made a few attempts with the wiring to split it around the screw neatly.

I will check that.

Thanks Gavin

If it is that, I for one would still advise you get that junction box sorted sooner rather than later, particularly as it's easy to forget where such things are placed.
 
I was wondering that?
maybe was a disagree because it shouldn’t have ever been buried as burying the joint effectively removes the safe zones to run the cable in?
I thought regulation stipulates that if its inaccessible it must be MF not that it must be accessible full stop, I agree joints behind plaster is less than ideal. I've never had to make a joint to be set behind plaster so be good to know...
 
I thought regulation stipulates that if its inaccessible it must be MF not that it must be accessible full stop, I agree joints behind plaster is less than ideal. I've never had to make a joint to be set behind plaster so be good to know...
Yeah I think a maintenance free box would be technically ok buried in plaster as long as it had good enough IP rating to prevent the plaster ending up in the box.
But if you remove the accessory that it used to be there then there is no indication that a cable and subsequently a junction Box are there Because by removing the accessory you have removed the thing that you “measure” the safe zones from if the accessory that you remove was say in line with another socket you’d be ok but in my experience those big ugly cooker switches tend to be mounted significantly higher than the sockets so you could end up with a cable running down the wall not in any safe zone.
 
Last edited:
Yeah I think a maintenance free box would be ok buried in plaster as long as it had good IP rating to prevent the plaster ending up in the box.
But if you remove the accessory that it used to be there then there is no indication that a cable and subsequently a junction Box are there Because by removing the accessory you have removed the thing that you “measure” the safe zones from if the accessory that you remove was say in line with another socket you’d be ok but in my experience those big ugly cooker switches tend to be mounted significantly higher than the sockets so you could end up with a cable running down the wall not in any safe zone
Yea as I said I agree less than ideal, I suppose I depends how far it's being moved as well... 3" or 4" not so bad 12+"... Not sure why I got a disagree for it though @123
 
Yea as I said I agree less than ideal, I suppose I depends how far it's being moved as well... 3" or 4" not so bad 12+"... Not sure why I got a disagree for it though @123
There will be 101 better ways to do it like MF JB in the ceiling under the floor or even a screw type JB in the attic. Personally when I stick a JB anywhere even if it’s MF I like to make sure it can still be accessed even if there is no requirements for it to be I’ve seen “wago type” connectors either knock offs or other legitimate brands fail spectacularly, so even with MF it probably isn’t the best of ideas to make it totally inaccessible.
 

Reply to New electric cooker causing power to trip at fuse. The fuse is reluctant to flick back on after. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
817
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
798
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...
Replies
8
Views
877

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock