Hi guys new to the forum after bit of advice. My family are installing a new shed in the garden and require a lot of power ie few sockets, lights. I am planning of running a swa fed from 32a mcb from the main board to a sub board.
Have a question-
Shall I install the new 32a mcb in the main board on the RCD side or main switch side?
Thanks
 
You should always earth the Armour
I was not suggesting that they shouldn't, but I'm sure there's a lot of SWA with no earth on the armour.
You wouldn't get any of the benefits of SWA but you'd still get the cost, so it'd be pointless to install RCD protected SWA where normal multi core cable would be allowed.
 
Thanks for the replies guys, I was planning on using swa because because it's going to be run external but clip direct not buried at any point.
I did think RCD only at the sub board would be the best setup.
Earthing arrangement is TN-CS
Now the issue with earthing the armour is the main board is plastic so the 'o ring' would be useless but it will be done on the new sub board. Earthing will be identified using the black core both ends.
 
73661.jpg
 
I might be wrong but im assuming the op is not an electrician as some of his replies are lacking even basic knowledge.
I am surprised the thread is open still as i can see it turning into us designing the whole job.
No mention of how he is getting this signed of by an electrician of bc to comply with part p either
 
Yes, you must connect the SWA to the installation earthing system at the supply end.
You should see that when you do your design FMEA.
I'm not an electrician but do you mean the physical connection must be at the supply end, or just that the armour has to be connected to the earthing system that protects it?
I guess you're suggesting if the cable is cleanly cut quickly enough (5s disconnection time) it may leave an unprotected live conductor physically separated from the cpc that protects it, and possibly shorted to the now floating armour.
 
I'm not an electrician but do you mean the physical connection must be at the supply end, or just that the armour has to be connected to the earthing system that protects it?
I guess you're suggesting if the cable is cleanly cut quickly enough (5s disconnection time) it may leave an unprotected live conductor physically separated from the cpc that protects it, and possibly shorted to the now floating armour.
One potential failure mode yes.
 
There are occasions when earthing the armour [when a seperate cpc exists in the cable] can only be carried out at the 'load' end and I can't see any reason why this is detrimental to safety when done correctly. I wish people would stop posting misleading nonsense. :rolleyes:
What are these occasions then?
 
What absolute carp.

Proper regs numbers to back up your somewhat dubious claims please

Or do we need a new rating “fake reg”
Murdoch they are proper regulation numbers, you are now just showing your ignorance.
BS 7671 is not the be all and end all.
These are the Regulations that you will be prosecuted under.
BS 7671 is your Regulation 29 defence if followed.
 
Hum ...

I think you need to calm down and go back and answer the original point again.

There is no law stating that swa must be earthed at the supply end ...

The question was what is the BS 7671 reg number that you believe refers this to
No your question was, what REGULATION, you actually said in post #23 "Reg number please"
Which I then gave you and since then you have been disagreeing with me.
You said NOTHING about BS 7671, you asked for a Regulation, not a clause in a standard.
Remember, Regulations are law, BS 7671 is a standard.
The numbers I quoted are the law that you would be in breach of.
Try THE, Electricity At Work Regulations 1989 (As Amended).
Also if you want clauses from some industry guidance try...
522.6.201, .202, .203, .204
522.8.10
543.3
IET GN8 guides you to EAWR on this topic just for your guidance.
 
Is it not just common sense that it should be earthed at the supply end? What if it got severed completely and then re-energised, the armour would not be earthed. Mind you round here there is loads of it not earthed at all, seems to be a bit of a blind spot with a lot of contractors.
 
The EAWR does not apply to a domestic installation.
SWA should be earthed, otherwise it won’t work as designed.
It should a earthed or connected to the same earthing system as used by the protective device protecting the SWA.
Connecting the armour to one of the cores at the load end of the cable would require the Zs measurement would have to be taken at the supply end of the armour.
Not sure whether the Zs would then be low enough for the protective device to operate?
 
i think EAWR does apply to domestic installations, inasmuch as during any works carried out on the installation, and also the fact that you could consider housewives ( and house husbands for the PC loonies) to be working, even if only using a dishwasher. tin hat secured with cable ties and a bit of sticky tape.
 
Sorry but no.
The EAWR applies to employees and self employed persons while they are carrying out work tasks.
The only time a domestic installation would fall within the remit of the EAWR is if there were servants or domestic staff working there.
The EAWR would not apply to the installation, but would apply to the work practices of a tradesperson working in a domestic installation.
 
i agree. with that. myhousewife analogy may be a bit misleading, but it applies not only to the electrician working there on the installation, but to the safety of other trades e.g. tilers, woodbutchers, gas fitters, etc. ( sod plumbers, they don't deserve consideration. :D:D:D.).
 
We work to bs7671 in normal installations. As long as the disconnection time is met there is only a requirment to earth a conductive part that is part of a cable, no set in stone requirement of where. Nobody is ever going to be prosecuted for earthing at the load end and meeting ADS requirements,and to suggest so is ridiculous.
For small SWA cables (1.5/2.5/4.0 etc) with a cpc on shortish runs I'll frequently banjo one end only, whichever end is most convenient. I can see no point in making additional work doing both ends. Longer runs and larger distribution circuits with higher fault currents I'll do both ends.
NICEIC AC and our inspector has never queried it.
 
New posts

Reply to New sub board for shed swa advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to get the lionshare of a small shed wired before a friendly electrician does the needful. I'm a confident DIYer, but I would...
Replies
25
Views
1K
Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
789
Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock