last "whole house dead" i was on, L-N 0V, L-E 240V. hence all L and N conductors in the house were "live", nothing worked. I isolated at Main Isolator and called Scottish Power. was a failed N joint where customer's supply was tapped off underground in street. SP started digging at 6pm. supply back on by 8pm.
 
The 3036 should be selective with the DNO fuse, certainly at a 2:1 sort of ratio (30A and 63A or more BS88) to faults of 0.5kA or so. But I would have doubts if the PFC is very large given the modest break rating of the 3036, and even more fundamentally the possibility that someone has already changed the 30A wire for whatever but of mid-sized copper to hand.

Personally I would always change for the Wylex MCB replacements if a CU change is currently unaffordable, so much less trouble to reset than Joe Public trying to rewire a fuse (often in the dark) and no risk of wrong size replacement wire.
 
Over my 40+ years in the industry I have seen the DNO fuse blow without the local OCPD blowing or tripping a handful of times. The last time was about 7 - 8 years ago an old rubber cable gave up, it shorted took the DNO fuse and caused a fire and left the 3036 30A fuse intact
Most of the times it was a rewireable cut out fuse that blew so the whole service head was changed
 
Looking at the plots for BS 3036 fuses in the regs (p365 & p366) by time you get to 0.1s the curves are looking like "constant I2t" region (they are sloping down at 2 decades of time per decade of current on the log-log scale) and using the tabulated values for current at 0.1s blowing time I get:
  • 20A = 260A * 260A * 0.1s = 6.8kA A2s
  • 30A = 20kA
  • 45A = 81kA
Looking up one of the data sheets I have for Mersen BS88 LV fuse links they have the pre-arcing I2t for a 100A fuse as 14kA so in fact a 30A rewireable fuse is able to get a 100A HRC fuse beyond the point of no return on an adequately large fault.
 

Reply to No power to whole house after water fell on to cooker??? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
741
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
792
In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
371
I have a detached garage with a 60 AMP subpanel which has lost power. I traced the failure to the wire running under the walkway via conduit...
Replies
3
Views
771
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
210

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock