I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
 
I was also under the impression from the draft that only dwellings would require RCD protection for lighting circuits regardless of installation method.

Not yet got my book though so can't check.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
You are carrying out EICRs to the 18th Ed?
 
He’s correct it’s for dwellings
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
Very worrying.
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
B*gg*r! Yep your correct.
Pleased I haven't sent the EICR yet.
Also really pleased I'm part of forum. Could of been a changer there.
I don't like giving false information to clients, not good for my reputation.

Feel a bit embarrassed now. Why did I think this!
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.

Another stupid regulation.

Why not in commercial premises?
 
Why not in commercial premises?

Because lamps are more likely to be changed by maintenance teams than clumsy (or infirm) householders, who are at more risk poking around in ES fittings without knowledge of safe isolation etc.

And the original fault - C2 if the fittings aren't actually live. Otherwise there's no way to indicate a higher risk scenario of the fittings being live and ready to zap someone.
 
Because lamps are more likely to be changed by maintenance teams than clumsy (or infirm) householders, who are at more risk poking around in ES fittings without knowledge of safe isolation etc.

And the original fault - C2 if the fittings aren't actually live. Otherwise there's no way to indicate a higher risk scenario of the fittings being live and ready to zap someone.

I've given you a disagree, because I simply see it as another example of clutching at straws to make enough changes to justify the 18th edition plus the vested interests of manufacturers on these committees who see increased revenues AND profits.
 

Reply to Opinions please EICR code C1 or C2? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock