Only in a dwelling.
Really .... Reg number?
Discuss Opinions please EICR code C1 or C2? in the UK Electrical Forum area at ElectriciansForums.net
Only in a dwelling.
You are carrying out EICRs to the 18th Ed?I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.
I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.
I will look up reg when get a chance.
He’s correct it’s for dwellingsReally .... Reg number?
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcdHe’s correct it’s for dwellings
Very worrying.I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.
I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.
I will look up reg when get a chance.
YesYou are carrying out EICRs to the 18th Ed?
B*gg*r! Yep your correct.Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd
To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd
To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
Why? Doesn't come into effect until 01/01/19.
During transitional period we can use either. So I give the customer the option.Why? Doesn't come into effect until 01/01/19.
During transitional period we can use either. So I give the customer the option.
This customer chose 18th.
Why not in commercial premises?
Because lamps are more likely to be changed by maintenance teams than clumsy (or infirm) householders, who are at more risk poking around in ES fittings without knowledge of safe isolation etc.
And the original fault - C2 if the fittings aren't actually live. Otherwise there's no way to indicate a higher risk scenario of the fittings being live and ready to zap someone.