peterhyper

-
Esteemed
Reaction score
411
A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
 
Last edited:
OP mentioned steel strands connected to light's earth. i assume they have earth terminals and so would be classI.
 
The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),



There is also no RCD protection for any external lights.

You got any photos of the SWA terminations you have mentioned?

Why do you think the lights require RCD/RCBO protection?
 
Thanks guys. Yes they are class 1 fittings. I have pictures on my mobile, but they will only show a couple or so strands of the swa connected into a terminal block and the lights cpc connected to the terminal blocks.

With regards the rcd, I would always fit or recommend an rcd be fitted to external lights especially when they are low level wall height and people brushing past and touching them is very likely. For the small cost involved fitting an rcd I believe it's worth it.
 
So the earth is terminated externally to the light fitting via a connector block? If so how does the earth enter the light fitting?
 
A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
Page 165 Blue OSG give a fairy comprehensive guide to EICR codes read and inwardly digest.
 
A block of flats has various external lights not just attached to the building but around the grounds. Part of the circuit has twin and earth going underground with good readings but clearly unsuitable cable for external/underground use (not contained in any form of conduit).

The swa on the circuit is 2 core but the steel wire has been cut short on some lights at the top of brick piers with a couple of rusty strands of it attached to terminal blocks to connect to the lights earth, and not surprisingly the steel wire reading as the cpc as good as non existent with silly results (so the cpc is a 100% fail),

There are other ground lights that also have 2 core swa and the steel wire is not earthed (zero reading).

There is also no RCD protection for any external lights.

I am swaying between C1 and C2, so opinions appreciated.
Page 165 Blue OSG give a fairy comprehensive guide to EICR codes read and inwardly digest.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
 
I was also under the impression from the draft that only dwellings would require RCD protection for lighting circuits regardless of installation method.

Not yet got my book though so can't check.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
You are carrying out EICRs to the 18th Ed?
 
He’s correct it’s for dwellings
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
 
I was under the impression rcd protection on lighting circuit in 18th edition is not just limited to dwellings only.

I've just C3 ed a whare house lighting circuit on an EICR that has no RCD protection as I am carrying out works to the 18th now. Client doesn't have to do anything as it won't give an unsatisfactory.

I will look up reg when get a chance.
Very worrying.
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.
B*gg*r! Yep your correct.
Pleased I haven't sent the EICR yet.
Also really pleased I'm part of forum. Could of been a changer there.
I don't like giving false information to clients, not good for my reputation.

Feel a bit embarrassed now. Why did I think this!
 
Any circuit supplying luminaries in a dwelling requires additional protection via 30mA rcd

To align with the base CLC Harmonised Document, the new Regulation 411.3.4requires the provision of additional protection by RCD for AC final circuits supplying luminaires within domestic (household) premises.

Another stupid regulation.

Why not in commercial premises?
 
Why not in commercial premises?

Because lamps are more likely to be changed by maintenance teams than clumsy (or infirm) householders, who are at more risk poking around in ES fittings without knowledge of safe isolation etc.

And the original fault - C2 if the fittings aren't actually live. Otherwise there's no way to indicate a higher risk scenario of the fittings being live and ready to zap someone.
 
Because lamps are more likely to be changed by maintenance teams than clumsy (or infirm) householders, who are at more risk poking around in ES fittings without knowledge of safe isolation etc.

And the original fault - C2 if the fittings aren't actually live. Otherwise there's no way to indicate a higher risk scenario of the fittings being live and ready to zap someone.

I've given you a disagree, because I simply see it as another example of clutching at straws to make enough changes to justify the 18th edition plus the vested interests of manufacturers on these committees who see increased revenues AND profits.
 

Reply to Opinions please EICR code C1 or C2? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
782
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
884
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Morning, Company had an external contractor coming in to complete an EICR recently. They have gave us the report with a C2 for holes in trunking...
Replies
22
Views
3K
Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock