If the Spur has come of a ring or radial with 13A sockets it will need to be RCD protected because you have altered or added on to an existing circuit thus you need to bring the whole circuit up to current regs.
411.3.3 (I)gives you al the info you need
please note there are ecseptions to this. If you have a good reason why the circuit should not be RCD protected and have carried out a risk assesment.
however the definition of a good reason is debatable.
In in a dwelling risk assessments are not permitted therefore exclusion of RCD's are not accepted for this reason.
another exception is a suitably identified socket outlet provided for connection of a particular item of equipment. So this may be your exemption on the alarm. However if there are other 13a sockets on that circuit it will need to be RCD protected.
Why does the whole circuit need RCD/RCBO protection?