Hi all. Our house has a Bosch double oven which is rated at 4.4kW and a Bosch induction hob which is rated at 7.2kW. The hob is on it's own dedicated circuit. The oven however is connected to the same ring main as the 13A sockets via a 20A DP switch which runs with a 32A rcd as well. :confused::confused: Will this cause problems? Should the oven be on it's own dedicated circuit?
 
As Paul said and the problem is that when you put the oven on and there are other appliances in operation on the ring the demand will be too big and it will trip out your mcb / rcbo.

However, if the oven is within 2metres (horizontally) of the hob isolator there is a very good chance (taking diversity into account) that the radial that supplies the hob could also supply the oven. Will depend on the length of the run and thickness of the cable.
 

Reply to Oven installation in the Australia area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
666
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
841
Here is my situation We have a dedicated oven circuit in our house with a 40A RCBO We have bought a dual fuel range cooker which states it has a...
Replies
0
Views
835
Hi all, I've recently had an oven installed by AO and afterwards I noticed in the installation instructions that the electrical connection needed...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock