Hi all, I'm fairly new to all this so bear with me if it's a ridiculous question...

In my text book that I'm studying for my course (c&g 2365) it has symbols that you use to define whether the protective device will work for a given circuit (I think? please correct me if I'm wrong).

The symbols are
Iz (current carrying capacity of conductor)
It (value of current stated in regs for type of cable and install in amb temp of 30c)
Ib (current intended to be carried by circuit)
I2 (operating current of protective device)

Then it gives me a formula of conditions that must be satisfied for circuit

Ib<In<Iz and I2<1.45 x Iz

Where does the In come from? Am I being stupid?
And also how would you work out much current appliances and cookers will use on a circuit?

Thanks
 
In is the rating of the fuse/MCB. so that Ib<In (so the ocpd won't trip zt normal load). and In< Iz ( so that the ocpd will trip before the cable is overloaded). I2 is the current which will cause the ocpd to trip ( as ocpd's will stand overload. I2 is generally 1.45 x In).
 
Hi all, I'm fairly new to all this so bear with me if it's a ridiculous question...

In my text book that I'm studying for my course (c&g 2365) it has symbols that you use to define whether the protective device will work for a given circuit (I think? please correct me if I'm wrong).

The symbols are
Iz (current carrying capacity of conductor)
It (value of current stated in regs for type of cable and install in amb temp of 30c)
Ib (current intended to be carried by circuit)
I2 (operating current of protective device)

Then it gives me a formula of conditions that must be satisfied for circuit

Ib<In<Iz and I2<1.45 x Iz

Where does the In come from? Am I being stupid?
And also how would you work out much current appliances and cookers will use on a circuit?
Thanks

In = nominal rating of overcurrent protective device.

appliances usually come with the Kw rating attached. use the formula I = P/V to work out the current demand. remember to apply diversity where allowed.
 
Thank you very much! That makes much better sense. Became pretty obvious once you said it! Haha
So if you have numerous appliances on a circuit is the total current all of them added together?
Thanks again!
 
Thank you very much! That makes much better sense. Became pretty obvious once you said it! Haha
So if you have numerous appliances on a circuit is the total current all of them added together?
Thanks again!

Yes, but note Shagbite's reminder to to apply diversity where allowable.
 

Reply to overcurrent protection question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello! I'm struggling to find an answer to this question online. I'm new here btw - I'm a DIYer with a physics degree Currently when my fridge...
Replies
19
Views
1K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Hi I'm currently doing C&G 2365 Level 3 I'm working through the 305 design assignment (Swimming pool, hotel etc.) Other then this assignment I...
Replies
5
Views
4K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock