Discuss Parallel paths on R1 + R2 test in the UK Electrical Forum area at ElectriciansForums.net

DaveS

-
Reaction score
24
Hi there

Doing some testing at moment. R1 + R2 readings coming in lower than R1 + Rn. Cpc neutral and live all disconnected. There is alot of containment on job and adaptable boxes are all fly leaded to earth. My thoughts are they are parallel earth paths but guy working with seems to think because cpc disconnected at board it can' be. Who is right basically? Thanks
 
Hi there

Doing some testing at moment. R1 + R2 readings coming in lower than R1 + Rn. Cpc neutral and live all disconnected. There is alot of containment on job and adaptable boxes are all fly leaded to earth. My thoughts are they are parallel earth paths but guy working with seems to think because cpc disconnected at board it can' be. Who is right basically? Thanks
What are the r1, rn and r2 readings?
 
He is in regard to they cannot be parallel paths to earth, but you are in regard to there may be parallel paths between junction boxes or back boxes dependant on the type on cable management and building structure.
 
0.92 on r1 + r2 and 1.25 on the r1 + rn both wired in 2.5mm
Don't think you understood my question Dave end to end readings r1,r2 and rn as seperate conductors, as described in the RFC testing procedure. From your statement the circuit is wired in singles 2.5mm2,
It could be that you have a poor connection in one of the conductors, proving the end to end resistances will settle the arguement.
Are you nulling the leads at the ends of each test?
 
Last edited:
if it's in metal containment that will provide a parallel earth so the R2 reading will be the cpc and metalwork in parallel.thus giving a lower reading.
 
Don't think you understood my question Dave end to end readings r1,r2 and rn as seperate conductors, as described in the RFC testing procedure. From your statement the circuit is wired in singles 2.5mm2,
It could be that you have a poor connection in one of the conductors, proving the end to end resistances will settle the arguement.
Are you nulling the leads at the ends of each test?
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
You can do end to end testing at the CU Dave
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?

I'm confused how this could affect the carrying out of end-to-end readings. I might be missing something.
 
Ah, you never said. Must admit I assumed RFC. Multiple floors doesn't affect testing though still.
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
End to end readings are for RFCs, this is where the confusion comes from, if you had mentioned that it was a lighting circuit the confusion would have come to the for earlier, you may need to brush up on your testing procedures Mate, the question begs, how did you get your R2+R2 results?
 
Hi Pete I don' think I can do end to end readings as over multiple floors? The leads were nulled yes. Have just tested a seperate circuit and how similar readings with a 0.30 lower difference again with r1 + r2 this does parallel paths no?
End to end readings are for RFCs, this is where the confusion comes from, if you had mentioned that it was a lighting circuit the confusion would have come to the for earlier, you may need to brush up on your testing procedures Mate, the question begs, how did you get your R2+R2 results? Message to oneself don't assume anything or that anyone knows what they are doing.
 
Now we know it is a radial then yes any metal containment will affect readings due to parallel paths unless you isolate the cpc from the containment. Disconnecting the cpc at the board will have little effect unless the cpc goes to a single point of utilization.
 
Now we know it is a radial then yes any metal containment will affect readings due to parallel paths unless you isolate the cpc from the containment. Disconnecting the cpc at the board will have little effect unless the cpc goes to a single point of utilization.
Deleted
 
Hi there

Doing some testing at moment. R1 + R2 readings coming in lower than R1 + Rn. Cpc neutral and live all disconnected. There is alot of containment on job and adaptable boxes are all fly leaded to earth. My thoughts are they are parallel earth paths but guy working with seems to think because cpc disconnected at board it can' be. Who is right basically? Thanks
There could be parallel paths if the conduits are straight into the board or into trunking and the trunking is bonded and the building structure can also create a parallel path to earth
 

Reply to Parallel paths on R1 + R2 test in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hello, Hoping to get some advice on R1 + R2 radial testing and best practise. When doing R1 R2 instead of taking cables from mcbs/rcbos and the...
Replies
1
Views
2K
Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
834

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock