went to carry out a periodic report today and noted the points below. what are everyones thoughts on the coding?

1. no earth connected to metal light fitting. earth in cable but not on light. Code 2
2. twin and earth cable in roof space. property being thatched roof no rodent protection. No code
3. no 30ma rcd protection to ground floor sockets. socket could be used outside. Code 2 (or code 4 100mA RCD is useful probably not a very bad shock)
4. no fan isolator in downstaires toilet. no window No code
5. socket over cooker. plug lead over above hob on double socket. Code 2
6. cooker cable not clipped to surface from isolator to switch. Code 4
7. no main earth bond on oil pipe. Code 2

The supply is from over head but could not find any earthing stake as main earth. disconnected bonding to water and found out that the earth was from the pipe work in the house being cross bonded. phoned electricity company and sending someone out to see if they can convert to pme (tncs). Am I right in asking them first to convert as it is their property. Something you should discuss with customer first unless you have been told to do all remedial works, PIR is recommendation not action. Certainly a good idea but may well cost.

going back tomorrow so will find out what the electricity company say.

what codings would everyone say the points are.

thanks.
Nothing requires further investigation so no code 3s.
 

Reply to PIR coding help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
829
Hi, Heavy industrial spark here, never do house bashing hence the question. I currently have a light switch at the front door not doing anything...
Replies
1
Views
444
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
951
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock