Discuss Poor install EICR 12 year old hotel in the UK Electrical Forum area at ElectriciansForums.net

Again reading the napit codebreakers book it states holes not made goot as to reduce the spread of fire are C2. I would rather C2 and have a valid reference such as a book than to C3 it and argue against it.
There is no right or wrong answer its down to the persifics of each situation and you make a judgment call on it I will stick with my code 3 but would not judge someone else if they where to code 2 it .
 
The idea is tho that you are now outside the equipotential bonding using outdoor equipment so I’d agree that if socket outlets that are not likely to be used outdoors and this is carefull considered by the inspector perhaps in conjunction with the client, then I agree a C3 at worst for no rcd protection to sockets.
You are coding against additional protection to the user and not the equipment plugged into it
For a specific socket used as in the op for a fridge it can’t possibly be a C2 code
The sockets are not labelled, no risk assessment and they are not being used for the fridges in alot of the rooms. The client also said that he often finds the fridges have been unplugged as there isnt enough sockets in the rooms
 
If the swa is glanded at the supply end and the armour is at least connected to earth, I can’t see how it can possibly be a C2 unless there is signs of mechanical stresses on the cable at the load end?
Cant see above the DB to see if its cleated well and they all seam to be coming in at angles. Its all together rough so ill stick with C2. If i was to share some of the communal areas you would agree. The rooms are good compared.
 
There is no right or wrong answer its down to the persifics of each situation and you make a judgment call on it I will stick with my code 3 but would not judge someone else if they where to code 2 it .
I think youd agree that it is rough and would prefer to see the DB installed properly and stick an rcd socket on the socket not protected as again the client has stated people unplug the fridge and use it for all sorts.
Does it give a reason for this? , also is a hotel classed as commercial I thought they would be classed as simply a hotel
Yes its classed as commercial premesis.
 
Regarding the socket, it's a code 3 for me, however in these circumstances I always add an advisory note that the provision of RCD protection is strongly recommended. Given that under a very recent edition of Bs7671 the provision of a socket outlet for a specific item of equipment was permitted without RCD protection it is very hard to justify a 'potentially dangerous' code.
 
Regarding the socket, it's a code 3 for me, however in these circumstances I always add an advisory note that the provision of RCD protection is strongly recommended. Given that under a very recent edition of Bs7671 the provision of a socket outlet for a specific item of equipment was permitted without RCD protection it is very hard to justify a 'potentially dangerous' code.
But the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
 
It’s the 18th now.
All socket-outlets must have RCD protection.
Risk Assessments are out the window.
Risk assessments are not out of the window on non domestic installations 411.3.3 an exception to (i) is permitted where other than an installation in a dwelling, a documented risk assessment determines that rcd protection is not necessary
 
But the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
The regulations do not differ on who is using the sockets so you can’t make that argument
The fact that a documented risk assessment can be used on non domestic installations gives, if anything gives a bit of a relaxation on 411.3.3
 
Last edited:
The regulations do not differ on who is using the sockets so you can’t make that argument
The fact that a documented risk assessment can be used on non domestic installations gives, if anything gives a bit of a relaxation on 411.3.3

Screenshot_2019-01-04-21-07-18.png
 
But the reg 411.3.3 specifically says risk assessment required and even if ther was its clearly not being used for a specific item of equipment. I still think C2 when the public are involved especially in terms of liability.
The regulations do not differ on who is using the sockets so you can’t make that argument
they do and can not speak for the whole industry.
I can show you an NICEIC similar list which is available to the online customers which gives a C3.
You see the problem
 
I walked into this in a cleaners cupboard in the hotel kitchen. Apparently been like this since it opened. I think you will take your sloppy workmanship statement back. The lid was wide open, i havnt opened it.

20180612_154903.jpg
 
I’ll imagine that someone’s been using that as a locker! They probably keep the 5mm retaining bolts on a keychain!
Nice to see proper blanks being used!
 
Risk assessments are not out of the window on non domestic installations 411.3.3 an exception to (i) is permitted where other than an installation in a dwelling, a documented risk assessment determines that rcd protection is not necessary
I stand corrected, thought that was being dropped.
At least they’ve took on board that the RA must determine “RCD protection is not necessary”.
 
I note that the Hotel is 12 years old, which means it was designed to the 16th edition.
As such RCD protection was not required unless it could reasonably be assumed that the sockets would be used to provide power to portable equipment used outdoors.
If the inspection is being conducted in accordance with BS7671, then the lack of RCD protection would be a code C3 (complied at the time of design/construction).
 

Reply to Poor install EICR 12 year old hotel in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
306
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hi I am carrying out an EICR. I have a garage mini sub DB supplied via 2 x 2.5mm T&E equivalent 5.0mm protected at main DB by a 32A mcb. I know...
Replies
8
Views
1K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock