Hi all need some help,
I was called to a job to do some rectification work after a so called sparkey half wired a house.
He decided to run a 10mm T+E from a Henley block located in a cellar to a second C/U three floors up, I'm going to have to change the 10mm to 16mm.
My question is what do I use as a protective device once I have started remedial work. I was going to use a 63A switch fuse however the cable runs through stud walls so could do with it being rcd protected too.
Been racking my brains but I think I have over complicated it for myself.
 
whats the expected load of this 3rd floor ?

what diversity are you applying ?

looking in my OSG shows that 10mm t&e ref C carries............





wait for it..........






64A !
amazing lol !

and even if you have to de-rate the cable , would 50A not do the job so you can keep the cable and keep costs down for the customer ?
 
another point is the bonding. if required, might need a separate bonding conductor.
 
The customer has plans to add more circuit at a later date but isn't sure when he wants to do it hence the 16mm rather do it now rather than later. However you're right about the 64A that was never in doubt.
However my question still remains unanswered as to what to use to protect the cable running up.
If it was in a commercial or industrial set up I'd use a switch fuse.
However I'm uncertain in this case.
 
only needs RCD if buried in wall/s <50mm etc.
 
if you're going to uprate to 16mm, then go with dilb and SWA. then you get a decent cpc.
 
RCD in cellar, whole 3rd floor trips - whoops down you go. That said, it would be a good way to get fit and loose a few pounds when nuisance tripping starts!
 
My question would be why did the first spark only do half a Job? the customer may be a bad payer, I would find out who the first guy was and have a chat to him just in case. There is a bad spout of customers mentioned on here lately who do not like paying their bills, otherwise it does pain me to agree with what Biff said in post 2 lol
 
Hi all need some help,
I was called to a job to do some rectification work after a so called sparkey half wired a house.
He decided to run a 10mm T+E from a Henley block located in a cellar to a second C/U three floors up, I'm going to have to change the 10mm to 16mm.
My question is what do I use as a protective device once I have started remedial work. I was going to use a 63A switch fuse however the cable runs through stud walls so could do with it being rcd protected too.
Been racking my brains but I think I have over complicated it for myself.

I am always wary going to a job 'half done' by a previous electrician - you only have the customer's word on what happened (spark may not have received a stage payment or something).

The 10mm may prove to be ok - obviously no switchfuse but that may have been a later intention (had the previous guy finished the job).

Edit: MDJ - Got in before me! Damn my slow typing!!! :)
 

Reply to Protective device in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
770
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
983
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock