yes it would if a neutral shares between 2 circuits protected by 2 RCBO's then you find that both of the RCBO's will trip when a load is applied ,if this is the case most commonly in lighting circuits you need to identify which circuits have a shared or borrowed neutral by a process of elimination and testing
 
yes it would if a neutral shares between 2 circuits protected by 2 RCBO's then you find that both of the RCBO's will trip when a load is applied ,if this is the case most commonly in lighting circuits you need to identify which circuits have a shared or borrowed neutral by a process of elimination and testing

Thats what my mate said as well. But suely all the neutrals are connected together in the CU ? and as the rcbo's are single pole devices the neutrals will still be connected together even if one of them trips????
 
It's not about where the neutral ends up, it's the path that it takes to get there!
For a 30mA RCD or RCBO, the current going out down the line and returning down the neutral must be equal - if the imbalance exceeds 30mA it will trip.

So:
If your line current goes back to another neutral, you have an imbalance in both circuits - and if both are RCD'd, both RCDs will likely trip (though with something like a clock radio only drawing a few mA, maybe only one will trip)

Even though RCBOs are single pole devices in terms of overcurrent, switching and isolation, in order to work the neutral current for that circuit MUST flow through the toroid inside, so that the (hopefully) equal and opposite currents result in no current being applied to the trip solenoid.

simon.
 
Last edited by a moderator:
Ah yes they are connected in the CU but after ists gone through the electronics within the RCBO as wdmdl has said its the paths the neutrals take and the line and neutral must be equal, the RCBO/ RCD is perfectly balanced just like a set of scales so anything that changes the balance slightly ,incorrect neutral path earth leakage etc exceeding the 30 ma then the RCBO will trip
 
It's not about where the neutral ends up, it's the path that it takes to get there!
For a 30mA RCD or RCBO, the current going out down the line and returning down the neutral must be equal - if the imbalance exceeds 30mA it will trip.

So:
If your line current goes back to another neutral, you have an imbalance in both circuits - and if both are RCD'd, both RCDs will likely trip (though with something like a clock radio only drawing a few mA, maybe only one will trip)

Even though RCBOs are single pole devices in terms of overcurrent, switching and isolation, in order to work the neutral current for that circuit MUST flow through the toroid inside, so that the (hopefully) equal and opposite currents result in no current being applied to the trip solenoid.

simon.


I'm away to get some humble pie.........
 
1552044_f520.jpg
this may help
 

Reply to RCBO's and borrowed neutrals in the Australia area at ElectriciansForums.net

Similar Threads

I have a client with what appears to be an intermitent fault on the lighting, but trips the power. The installation has a 16th edition board with...
Replies
17
Views
2K
Hi, I have just replaced an old rewireable fuseboard with a 10way consumer unit with rcbo's fitted. The issue i have is that when i connect one of...
Replies
19
Views
2K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
884
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock