Hi all,

i have heard so much difference of opinion on this subject, and im sure it has been discussed many a time on this forum, but can anyone clarify a couple of questions i have on the subject please.

Do all new sockets installed have to be RCD protected, or is it only mandatory if they are likely to be used for powering anything outside or in a special location ?

When carrying out an electrical condition report, if none of the sockets installed have any RCD protection, would you put that down as a C1 code, or would you take into account the fact it was installed before the use of RCDs and was wired according to the regulations at that time and just put it down as a reccomendation to bring it inline with the current regs.
I have heard a few people say that its an instant fail, but im sure you have to give consideration to whn it was installed ?

Many thanks in advance
 
Hi all,

i have heard so much difference of opinion on this subject, and im sure it has been discussed many a time on this forum, but can anyone clarify a couple of questions i have on the subject please.

Do all new sockets installed have to be RCD protected, or is it only mandatory if they are likely to be used for powering anything outside or in a special location ? read bs7671 reg. 411.3.3

When carrying out an electrical condition report, if none of the sockets installed have any RCD protection, would you put that down as a C1 code, or would you take into account the fact it was installed before the use of RCDs and was wired according to the regulations at that time and just put it down as a reccomendation to bring it inline with the current regs. C2 if for use outside. otherwise a C3 if installed to previous regs. and compliant at the time.
I have heard a few people say that its an instant fail, but im sure you have to give considerationto whn it was installed ?

Many thanks in advance

my thoughts in red. for the 2nd answer,to the inspector as to whether or not in constites a real or poptential danger. though, it's always down
 
With regard to a condition report:-

as a minimum items installed prior to 7671:2008 without an RCD should be classified as C3 (improvement recommended). For me personally, if I enter a property that does not have any previous testing records (however obvious the age of the installation) then I would (using judgement) elevate such matters to a C2.

Obviously the installation premises type should give you a good idea of the level of protection required. If for example it was a hotel, and you were referring to the hotel rooms which are to be used by general members of the public then I would classify not having RCD protection on sockets a fail (C1 or C2) irrespective of previous testing records being satisfactory.
 
Hi thanks for your reply,

I wouldnt say i have lack of knowledge on the subject as I too would have coded it a C2 or C3, I just wanted to hear your opinions on here, as i recently had the debate with a guy who was Niceic registered and he was adament that if it didnt comply with the current regs you would put it down as a C1 if the sockets had no RCD protection.

I will be honest, im not as knowledgebale as some of you guys on here, but im no Electrical Trainee either and did a full 3years City and Guilds

I appreciate your feedback though
 
From the Electrical Safety Council guide;

Code C1
‘Danger present’. Risk of injury.
Immediate remedial action required.

Code C2

‘Potentially dangerous’.
Urgent remedial action required

Code C3

‘Improvement recommended’.


Can't see where a perfectly innocent Socket with no live wires hanging out of it can be a Code 1
 
Hi thanks for your reply,

I wouldnt say i have lack of knowledge on the subject as I too would have coded it a C2 or C3, I just wanted to hear your opinions on here, as i recently had the debate with a guy who was Niceic registered and he was adament that if it didnt comply with the current regs you would put it down as a C1 if the sockets had no RCD protection.

I will be honest, im not as knowledgebale as some of you guys on here, but im no Electrical Trainee either and did a full 3years City and Guilds

I appreciate your feedback though

Even still, your knowledge at this point it time is far too basic to be conducting periodic inspection and testing. Such a fundamental gap in your knowledge when it comes to design principles is evidence enough, and if someone doesn't know how to design, then they shouldn't be inspecting and testing. Going by some of your past posts you've only had your regs book for less than a year!

Do you hold a 2391 or 2394/2395 qualification? I'd steer well clear of EICRs fella, you could end up in a whole world of grief!
 
From the Electrical Safety Council guide;

Code C1
‘Danger present’. Risk of injury.
Immediate remedial action required.

Code C2

‘Potentially dangerous’.
Urgent remedial action required

Code C3

‘Improvement recommended’.


Can't see where a perfectly innocent Socket with no live wires hanging out of it can be a Code 1


Agree, but the inspector should be competent enough to determine 'when' a certain 'type of accessory' May be fit for purpose in one environment type and not fit for purpose in a different environment type.


On a lighter note, there is an argument to say that everything should be classified as a C2............Anything is potentially dangerous in the wrong hands! :)
 
It's only by learning that you can move forward

.I have seen many reports that that have failed a properly which I would have passed with less remedials
 

Reply to RCD on socket outlets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
845
Hi all, Just a quick one regarding the need for RCD protection for socket outlets rated up to and including 32A. I have been tasked to install...
Replies
17
Views
2K
Hi, just hoping for a bit of advice. When I travel abroad (Europe, predominantly Spain/Cyprus) I usually take a single travel adaptor and a UK 4...
Replies
2
Views
466
Hi, This post is about my concerns with medical IT socket outlets and want to alert you all if you are fitting them in a hospital. The current...
Replies
20
Views
2K
Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock