Hi everyone,

Quick question can you fit an RCD without any neutral connections?

If I have a 3 pole circuit breaker which has all 3 poles terminated with a 3 phase supply (L,L,L excluding neutral or earth) on the primary side and I am using only 2 phases on the secondary side (L,L) to create a 400v supply to a transformer, can I connect an RCD to this breaker?
 
I don’t think you can I have never seen a 3 pole (RCD) Residual Current Device and how could it work to detect earth faults which are single phase
 
Yes you can normally use a 3-phase 4-pole RCD without neutral, or on just two phases, but check the manufacturer's instructions as often the self-test button is only between specific lines so those terminals should be used to ensure it works.
 
I don’t think you can I have never seen a 3 pole (RCD) Residual Current Device and how could it work to detect earth faults which are single phase
The RCD just puts a sense transformer around all live lines used, so any imbalance is detected. As such the number of lines used has to be 2 or more so the legitimate return path is included.

Where it gets complicated is the self-test button on > 2 poles, and if the RCD needs a certain voltage on certain lines to function (i.e. more than just the energy of the fault current seen by the sense transformer). Type B RCD (DC sensing) need some form of supply for that aspect, but others like type AC/A often can trip on just a current.
 
The three pole is an mcb I assume, he wishes to connect an RCD from this?
The distribution board has 3 phases coming into it and is terminated to a 3 pole circuit breaker, but on the secondary side we are only using two phases. So wanted to know if I can connect an RCD to monitor the 2 phases.
 
Yes you can normally use a 3-phase 4-pole RCD without neutral, or on just two phases, but check the manufacturer's instructions as often the self-test button is only between specific lines so those terminals should be used to ensure it works.
Thanks for the response!!

Would this work with a set up of using a 3 pole breaker with 3 phases terminated on primary and only using 2 phases on the secondary, then connected a 4 pole RCD which only uses the two phases?

If the RCD senses load unbalance would this not end up tripping all the time as we are only using the two phases of the three?
 
Would this work with a set up of using a 3 pole breaker with 3 phases terminated on primary and only using 2 phases on the secondary, then connected a 4 pole RCD which only uses the two phases?
It should do. It might be better to put all 3*L from MCB to RCD if they are close together, just in case it has any future use.
If the RCD senses load unbalance would this not end up tripping all the time as we are only using the two phases of the three?
The RCD only cares that the sum of all currents is close to zero. So if L1 is the exact opposite of, say, L2 then the sum is zero and nothing trips. If L1 leaks to E or anything else, then L2 != L1 and if big enough difference it trips.

With a 3P only load like a motor, the current from L1 returns via both L2 and L3, etc. With a 3P+N load then you could have different SP loads from Ln to N, etc. In all cases what matters is the vector sum of L1+L2+L3+N is close to zero. If L3 and N are zero themselves, then you need L1 = -L2 which, if wired normally and all OK, is the case.
 

Reply to RCD without neutral 2 phase supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a question hoping I can get some help. I wanted to know if there is a 400V 3 phase supply (A/A/A) terminated on the primary side of a...
Replies
3
Views
887
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
759
Can we connect the 2 phases lines (110 V each) to RCD breaker? please advise ?
Replies
8
Views
674
Hello. How i should connect this 1 phase 2 pole 400v cooling pump? If i apply 1phase 230v and neutral it Will only growl and "spin" very very...
Replies
11
Views
712
Recently I have installed Type 2 Surge Protective Device SPD 20 to 40kA, Type1+2, Phase + Neutral + Earth (2 Pole 275 Volt AC) (Uc-275VAC...
Replies
7
Views
373

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock