Hello, was wondering what people thought about a cable supplying the farm buildings, i need to replace the cable so it now be a 16mm swa from service head area, across the garden and into the 1st shed, i was look ar brb and saw reg 705.411.1 (iii) which says all other circuits require 300ma rcd protection will this apply to the sub main cable or not.

many thanks
 
What earthing arrangements have you at the service head ?

If you have a TN arrangement you could in fact protect the SWA and do without the RCD protection for it.

That was my plan but the reg states : 'in all other circuits, RCD's with a rated residual current not exceeding 300ma'

My thoughts was if i was using a rcd to protect for the sub main cable then it had to be 300ma or less but im not as its tn system but it does say in all other circuits so still not sure.
 
Last edited by a moderator:
For what its worth, this is my interpretation:

For circuits with sockets less than 32A - 30mA RCD
For circuits with sockets greater than 32A - 100mA RCD
Everything else (including sub mains) - 300mA RCD

My guess, is that this is the RCD level for fire protection - farms usually store flammable materials
 
Thats what i thought as well just didnt want to have to buy a rcd to replace the switch fuse as it isnt on the farm until the cable enters the shed and then its goes striaght into the board.
 
If you look at reg 705.414.4 it classes residences and all other buildings as a farm installation,

I'm sorry jimmy I did make mistake about the RCD I was thinking of construction sites mate, and yes for any circuit in Agi you need to have RCD protection, sorry mate I took you down the wrong road there
 
so even with the earthed outer sheet of the armouring you still need to rcd protect the sub main ?

Will probably get shot down now , but the way i interpret it is yes .
We always bring the main tails in to a 100 to 300 ma s type before anything else, as yellowvan man put it, is how i see it too .
The type S is for discrimination , and we always TT all boards in the installation !
Would like to hear others opinions on how we do it ?
 
Last edited:
Will probably get shot down now , but the way i interpret it is yes .
We always bring the main tails in to a 100 to 300 ma s type before anything else, as yellowvan man put it, is how i see it too .
The type S is for discrimination , and we always TT all boards in the installation !
Would like to hear others opinions on how we do it ?

I normally bring the sub main from house and then tt everything from subboard onwards with s type 100ma but look like im gona have to start with rcd at source.

Do you also need to rcd protect the house with 300ma or less rcd, if yes how long has it been like that because ive not come across any yet
 
Hi,
See page 46 in GN7, this shows the supply installation main DB (incoming supply), and this diagram explains all, basically 300mA rcd's feeding all submains related to agricultural (out) buildings, whether this main DB happens to be located in a residential building or not.
 
Last edited:
Hi,
See page 46 in GN7, this shows the supply installation main DB (incoming supply), and this diagram explains all, basically 300mA rcd's feeding all submains related to agricultural (out) buildings, whether this main DB happens to be located in a residential building or not.
I agree, I was trying to point out that the house itself doesn't need the 300mA RCD.
 

Reply to RCD's on farms in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
I'm doing a college design project and need to choose a suitable range of circuit protective devices for the whole contact. I've chosen and...
Replies
7
Views
3K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
For context i am in my 2nd year in college and my head is going round in circles a question in my project for which i need to select the right...
Replies
22
Views
4K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock