My parents had an EICR completed after a change of tenant in the shop and flat property, this took place March 2021.

The summary of the report stated that the premises was dangerous and the full rewire was required to make it safe.

I have since completed a the C&G inspection and testing course through work and took a chance to have a look at the EICR given to us by our estate management firm.

I have noticed that the report does not contain any observations with the classification of C1 or C2 that would result in the requiring a full rewire. And also the inspector did not carry out any electrical tests to verify the condition of the existing installation (insulation resistance). The only observations included we C3 or FI all of which would not require a full rewire to make it safe.

There are also other mistakes and ommissions which suggest that the report was false and made to look like the premises was unsafe just to convince my parents that the wiring needed changing.

The inspector was contracted to carry out the EICR for the full premises which included a ground floor shop and first floor flat. I can only see information regarding the downstairs shop (DB1).

Now I am not suggesting that a week long course makes me an expert in EICR but it definitely makes me more aware of what to look for in a report.

We put our trust in the inspector and the l letting agent who recommended them.

My parents spent a lot of money on the full rewire and a second opinion has told us that the rewire was not required.

We believe that the inspector has acted unlawfully (breach of contract by not completing all tests included in the EICR, except limitations) and also immorraly. Both which means my parents paid out £8000 when it wasn't required.

The inspector is also a member of NAPIT so is obliged to carry out work to the proper electrical standard.

Does anyone else think we have sufficient recourse to make a complaint to trading standards, NAPIT and potential small claims?

I have attached the EICR for reference.

Thanks
 

Attachments

  • EICR Fail_1.jpg
    429.3 KB · Views: 63
  • EICR Fail_2.jpg
    538.6 KB · Views: 68
  • EICR Fail_3.jpg
    345.4 KB · Views: 63
  • EICR Fail_4.jpg
    298.9 KB · Views: 64
  • EICR Fail_5.jpg
    122.7 KB · Views: 58
  • EICR Fail_6.jpg
    475.4 KB · Views: 49
  • EICR Fail_7.jpg
    581.6 KB · Views: 46
  • EICR Fail_8.jpg
    391.9 KB · Views: 44
  • EICR Fail_9.jpg
    563 KB · Views: 60
If there’s no C1 or C2, then the EICR is satisfactory.
C3 doesn’t mean it’s unsafe, but as the shop is open to the public, then they would be trying to make it as safe as possible for the general public.

It could be argued that a rewire wasn’t needed, maybe just a new consumer unit to add rcd protection to the circuits.
 
If there’s no C1 or C2, then the EICR is satisfactory.
C3 doesn’t mean it’s unsafe, but as the shop is open to the public, then they would be trying to make it as safe as possible for the general public.

It could be argued that a rewire wasn’t needed, maybe just a new consumer unit to add rcd protection to the circuits.
Hi littlespark

Thanks for the reply.

I agree with what you say. I believe that the statement in section E should not have been made as a complete rewire was not the only remedy alongside the fact that the electrical system should have been marked as satisfactory.

Thanks
 
As littlespark has written above, no C1s or C2s = officially satisfactory.
I've recommended full rewires on many occasions where the installation is 'satisfactory', but this is always because there are so many alterations and extensions proposed to be made to that installation, that it would be easier, cheaper and give better results, to simply start again.
Assuming the new installation is similar in location and number of points to the original, then that does not apply here.
 
As littlespark has written above, no C1s or C2s = officially satisfactory.
I've recommended full rewires on many occasions where the installation is 'satisfactory', but this is always because there are so many alterations and extensions proposed to be made to that installation, that it would be easier, cheaper and give better results, to simply start again.
Assuming the new installation is similar in location and number of points to the original, then that does not apply here.
This EICR was due to a new tenant occupying the premises. No work was planned apart from what was said on the outcome of the EICR.

Since the EICR was carried out extensive rewiring was completed. All of which has been tested and Inspected.

As the initial EICR was completed incorrectly I believe that the rewiring was not necessary.

Thanks for your reply
 
Have you asked the inspector involved to comment?
No not yet. The original inspection took place in March 2021 and the rewire has since been completed.

I have spoken to the Citizens Advice but I was looking to see what other inspectors might think of the report.

I will probably contact the inspector to try and remedy it and look to putting a complaint to trading standards and NAPIT
 

Reply to Rewire after failed EICR. Have we been scammed? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
979
Looking for some advice and timescale here. I'm not an electrician just a tennet with a housing association. I've been offered top floor flat in a...
Replies
6
Views
505
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764
Hi, First time buyer here who is purchasing a 1970s 3 bed semi detached. No idea about anything electrical but the vendor said the electrics are...
Replies
13
Views
4K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock