Discuss Ring Final Tests in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
9
testing a ring final today
end to end test L 0.24 N 0.24 CPC 0.37
figure of 8 L1 -CPC 2 L2 - CPC 1 0.25
L1 - N 2 L2 - N 1 no reading
IR >999

cant figure out why open circuit on figure of 8 any answers?
 
So you have done your r1, r2 and rN and got satisfactory results, yes? I would hazard a guess that you are either making a mistake in connecting the figure of 8 or you have dodgy connections when taking readings
 
Check your instrument, test leads and adaptors for possible intermittent connections. Otherwise what you are claiming is that when connected in parallel the L & N (measuerd OK at 0.24Ω) both went open circuit at the same time. Also obviously the L/CPC reading was too high.
 
On my tester (Megger 1730), Continuity is always measured between the same two terminals (Red and Green), so to test continuity in a socket between live and neutral I need to change the tester terminals and plug the Neutral of the plug adapter into the terminal usually reserved for the CPC (Red plug lead into red on tester, and blue plug lead into green on tester). I hope this makes sense but did you change the inputs to the tester for failed test?
 
hang on. in the op you say you're not getting a reading L1 N2 etc. well, you should not. you are cross connecting the L's and cpc's so you should only get readings between these. the N's are not relevant.
 
hang on. in the op you say you're not getting a reading L1 N2 etc. well, you should not. you are cross connecting the L's and cpc's so you should only get readings between these. the N's are not relevant.
Think OP is referring to 'step 2' of RFC test, cross connection of live & neutral conductors to confirm correct connection of conductors at each outlet. According to his figures he should be obtain a reading of 0.12 ohms (0.24+0.24/4). Or have I misinterpreted both you & OP?

OP was your reading for r1+r2/4, 0.24, obtained at the CU ends. As Lucien said it's high, should be around 0.15ohms, although the reading for r2, should be around 0.40oms without parallel paths.
 
Sounds like a problem with the test procedure or interconnections to me. I can't see how you could have an open circuit if the end to end of both L & N conductors have continuity...? Or am I missing something also?
 
If I use the plug connector on my Metrel it will only test between the live pin and the earth pin. So for these tests I have to use an adapter that I can plug the leads in to manually.
 
As per Hightower - need an adapter plug with the Metrels. Daz
 

Reply to Ring Final Tests in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
391
After fixing a few CPC related issues on a ring final I got the following results L-L = 0.47 N-N = 0.47 CPC-CPC = 0.69 R1+R2 Tested at 0.31...
Replies
3
Views
1K
Hi so i am doing a test on sockets on a ring Final circuit for family member. Got my end to ends r1 0.62, rn 0.64, r2 0.97, identified opposite...
Replies
3
Views
2K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
629

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock