Discuss Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

The spur is 4.0 clipped direct so in theory if he uses the same size of cable and installation method as the existing he could add direct to it. Personally I would like to see it on its own circuit.
 
Ideally I'd like to add more sockets to the circuit in the garage

What are you intending to plug into these sockets.
Is the 32A breaker protected by an RCD?
 
The spur is 4.0 clipped direct so in theory if he uses the same size of cable and installation method as the existing he could add direct to it. Personally I would like to see it on its own circuit.
A spur equates to One double or single socket
A One fused or unfused spur unit
A One fusedspur feeding a Fixed appliance.
The only way you can add more than one socket is on a 4mm2 32 or 30 Amp radial circuit if adding more than one the the cable used must be the same as the circuit is wired in 4mm2, this is the same for a 20Radial circuit wired in 2.5mm2
As the circuit in question is a Ring FC adding more than one unfused socket is not allowed
 
if the CU is in the garage anyway, why not split the tails with \Henley blocks and fit a "garage board". RCD + 2/3 MCBs. then a fault in the garage will not saffect the house CU andyou would have a spare way/s. a 4mm 32A radial for sockets, 6A MCB for lights.....
 
Thanks.

Based on what's been said, is the following an acceptable way forward?

>Replace the existing twin socket with a fused spur unit, fused at 13 amps.
>Add additional sockets from the fused spur unit fed by 2.5.
 
This is somewhat unconventional and is clearly ad hoc, yes it should be on its own circuit as I have also suggested but the limitations of what can be added to this spur is clouded by the cable size, 4.0. Appendix 15 which is informative does not demonstrate the use of 4.0 cables/conductors.
 
This is somewhat unconventional and is clearly ad hoc, yes it should be on its own circuit as I have also suggested but the limitations of what can be added to this spur is clouded by the cable size, 4.0. Appendix 15 which is informative does not demonstrate the use of 4.0 cables/conductors.
 
Thanks.

Based on what's been said, is the following an acceptable way forward?

>Replace the existing twin socket with a fused spur unit, fused at 13 amps.
>Add additional sockets from the fused spur unit fed by 2.5.

Yes .... And it's going to need to be tested
 

Reply to Ring spurred at origin? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
Replies
11
Views
771
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
256
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
303
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
904

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock