tvrulesme

DIY
Reaction score
18
Looking at the electrical safe zones I can run cables within the top 150mm of a wall. I have a vaulted ceiling, would it be ok to run and clip my cables to the wall plate as seen in this image?

I don't think it will make a difference but this is for a lighting circuit, cables will be 1.5mm. They will be run in plastic conduit and plastered over.

wall-plate.png
 
If the wall plate is as shown in your pic, the cables look like they'll end up more than 50mm from the surface, when boarded, so will be free from safe zone regulations anyway.
 
If the wall plate is as shown in your pic, the cables look like they'll end up more than 50mm from the surface, when boarded, so will be free from safe zone regulations anyway.
Thanks a lot. Yes picture not super accurate so would be more like at the edge of the all. Does this mean it's not a safe zone?
 

Reply to Running cables next to wall plate in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

In preparation for an EVSE installation, I am running the supply cable from the main CU, via catenary, to a new CU in my garage. The cable is 6mm...
Replies
4
Views
209
Hi all, I am planning to install wall lights such as these ones (LAP Bronx Outdoor Up & Down Wall Light Black - Screwfix -...
Replies
5
Views
788
Hello I’m going to install a hard wired 230v security camera, incorporating floodlights, outside and above garage door onto brick. An exposed...
Replies
1
Views
1K
Hi there - good site. Mrs wants a new socket directly below a light switch on the ground floor (says it will look neater vertically inline)...
Replies
4
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
947

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top