Discuss safe isolation Am2 in the UK Electrical Forum area at ElectriciansForums.net

P

pablo4321

Hi to do safe isolation on my am2, this monday coming would this be correct procedure, this is a individual circuit, supplying a motor via a rotary switch.Could anyone advise me if this is correct,thanks in advance

identify circuit.
lock off put key in pocket and display warning sign.
check voltage tester for damage
check on proving unit
turn rotary switch to on position
go to motor check for voltage between all phases earths neutrals etc
then check again on proving unit
 
Hi to do safe isolation on my am2, this monday coming would this be correct procedure, this is a individual circuit, supplying a motor via a rotary switch.Could anyone advise me if this is correct,thanks in advance

identify circuit.
lock off put key in pocket and display warning sign.
check voltage tester for damage
check on proving unit
turn rotary switch to on position
go to motor check for voltage between all phases earths neutrals etc
then check again on proving unit
Seek permission to isolate
locate and identify equipment to be worked on
identify means of isolation
withdraw fuses.lock off isolating switches or circuit breakers
fit warning notices at point of isolation
select approved voltage indicating device
verify on proving unit or known supply
test all lines-line all lines- neutral all lines to earth and neutral to earth
if satisfactory re prove test indicator begin work
 
I find it helps to count the 10 steps when your testing the phases, at least you know if you've missed one out, tell the examiner and start again, no one wants to fail safe isolation but a lot do so I hear
 
Hi to do safe isolation on my am2, this monday coming would this be correct procedure, this is a individual circuit, supplying a motor via a rotary switch.Could anyone advise me if this is correct,thanks in advance

identify circuit.
lock off put key in pocket and display warning sign.
check voltage tester for damage
check on proving unit
turn rotary switch to on position
go to motor check for voltage between all phases earths neutrals etc
then check again on proving unit
Under exam conditions.....always state checking leads conforming to GS38
 
i dont really do much three phase so not sure, you test the end of circuit so would i turn dol starter on or rotary switch on then test at motor or test at rotary switch or dol starter thanks
 
Rotary isolator will be you isolation point, or the circuit OCPD.

The tests are in no particular order

L1-N
L2-N
L3-N
L1-L2
L1-L3
L2-L3
L1-E
L2-E
L3-E
N-E

Dont forget to lock off and prove you tester BEFORE and AFTER you have carried the above tests.
 
I imagine they will tell you what to isolate and also where to test. Isn't there a info booklet which you recurve before doing the AM2?
 
yes but doesnt say anything about it would i be right in thinking lock mcb for that circuit turn the rotary switch on and test the motor side just never done them before cheers
 
would you not turn the rotary switch on because if it was of and you locked wrong mcb off the power would only go to the switch and because it is turned of the power wouldnt be detected at motor
 

Reply to safe isolation Am2 in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I am looking for advice please. Last week I done my am2. And the only thing I failed on was safe isolation of the 3 phase circuit. The...
Replies
11
Views
5K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi Pretty new here, so not sure if this question goes into this thread I am not an electrician; however, I plan to integrate IOT devices and...
Replies
8
Views
1K
Hello, I have a EV charger that is reporting over voltage and is unable to charge. the charger will operate up to 253V The solar inverter reports...
Replies
6
Views
3K
Came accross a remedial whilst at work where a previous engineer had raised a job to investigate poss borrowed neutrals on a lighting db which...
Replies
2
Views
973

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock