Chris, this is the correct sized MCB for a 8.5kW shower, a 32amp device would be running at a slight overcurrent and although it would take a long time to trip it's not permitted in the regulations. I can't stand people who find fault with work unrelated to what they're doing - especially when they're spouting BS. :)
Thank you very much Dave for a very clear decision on this question.

Regards Chris
 
Dont think I agree there, if I saw a potentially dangerous situation I would point it out.

Saying that this is not a good example of that, as it's not a potentially dangerous situation.
So you are sure it is not dangerous because I think my tenant will still want it changed to a 32 because an electrician has told it is dangerous and must not use the shower.

Regards Chris
 
Rewinding to the beginning;

The tenant has just had a new cooker (delivered and ?) connected by an "Electrician".
Would this be from Currys or similar?
 
apart from all the good advice given so far, as long as the 6.0mm is installed as ref. method C, i.e. it can safely carry 47A, ( Ib<Iz ) then aas the shower is a fixed load, overcurrent protection is not required so a 50A MCB could be installed. 433.3.1 (ii). (BYB 17th).
 
So you are sure it is not dangerous because I think my tenant will still want it changed to a 32 because an electrician has told it is dangerous and must not use the shower.

Regards Chris
Without actually visiting the site for an inspection I cannot commit to a definate answer as to whether your installation is dangerous, however
Having a 32A or a40A mcb on an 8.5kw shower is quite common and I would not be concerned either way.
Obviously 40A Mcb is the preferred breaker.
 

Reply to Shower 8.5 on a 40mcb is it dangerous in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
759
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Replies
19
Views
2K
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
612
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
476

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock