Discuss Shower circuit on living room ring (Customer only want CU changed) in the UK Electrical Forum area at ElectriciansForums.net

robo83

-
Reaction score
40
Hi,

I visited a property today and after initial checks and before i go ahead with the quote i noticed that the shower (power shower) is supplied from the living room Ring.

I've informed the customer that this is not to regulations and requires its own supply. At the moment the customer doesn't want the new circuit installed for the shower and is expecting only a CU change.

How would you go about this and what actions would you take?

Regards,

Robo
 
If it was an electrically heated shower the customer probably would have noticed it tripping out by now.
A shower pump can be spurred off a socket final.
 
a new sherlock holmes mystery. the case of the disappearing OP.
 
Glad the op isn't inspecting my house. My power shower is on the lighting circuit and fed in 1.5mm t&e.
 
Glad the op isn't inspecting my house. My power shower is on the lighting circuit and fed in 1.5mm t&e.
me too mines on the upstairs ring manufacturers instruction says must be protected by a 3amp fuse , have not checked the load but im sure its only a couple of amps .
 
bloody southerners with posy showers indoors. no wonder you're all soft. :44:
 
My apologies for not replying sooner and incorrect information, i posted just before poping out.

The shower is an electrically heated shower, 7.2kw. At the moment no issues as there is minimal load on the rest of the ring.
 
Is it on a 32A ring?

7.2kw is about 31A. They must have very little else plugged in at the time the showers running.

Having said that, cables and protective devices can cope with much higher ratings than the max listed. How longs an average shower? 6-8mins??
 
My apologies for not replying sooner and incorrect information, i posted just before poping out.

The shower is an electrically heated shower, 7.2kw. At the moment no issues as there is minimal load on the rest of the ring.
You need to stress to the client, that the shower circuit needs to be wired in the correct size cable and own radial,before any CU change, either he agrees to disconnecting the shower if no remedial allowed, otherwise walk away.
 
Is it on a 32A ring?

7.2kw is about 31A. They must have very little else plugged in at the time the showers running.

Having said that, cables and protective devices can cope with much higher ratings than the max listed. How longs an average shower? 6-8mins??

There is only a TV and a few low voltage lights on the rest of the circuit.

You need to stress to the client, that the shower circuit needs to be wired in the correct size cable and own radial,before any CU change, either he agrees to disconnecting the shower if no remedial allowed, otherwise walk away.

Thanks for this advice, this was the opinion i was taking and going to let them know tomorrow.

My apologies again for the bad explanation on the first post, my focus of the thread was dealing with the customer. My opinion was of walking away, i have had very little dealings with domestic clients and mainly commercial.
 
so do electrically pumped showers generally use less power than a electrically heated shower?
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.
 
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.
He is not the op.?
 
With respect, that is worrying that you need to ask that when you are quoting for corrective works in someone's home. Also, there is issues with loading 7Kw from a single point of the ring, which from your other post, you don't see as an issue either. Genuinely, you should leave this one until you have more experience (which you will get), it is not being fair to the client mate.

with respect you should have gone to spec savers
 
so do electrically pumped showers generally use less power than a electrically heated shower?
There are some pumped and electrically heated showers, but they are, I believe, primarily manufactured for low water pressure supplies. Mira, for example produce some.
 
. How longs an average shower? 6-8mins??

I presume you don't have any teenage kids?........
Have a work with some people that do, you may want to rethink your times....... :)
 

Reply to Shower circuit on living room ring (Customer only want CU changed) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
772
Hi Customer has an extractor fan that’s inside the shower cubicle high up on the wall. The extractor fan has no form of isolation and is wired...
Replies
8
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
958
Bit of advise if anyone has time.. I have a customer who brought a new kitchen from wrens. Customer has had the route to the kitsch redecorated...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock