stidge

-
Arms
Reaction score
50
Hi all, Just had a phone call from customer telling me they are getting minor shocks when in shower and touching the controller/head.It is not an electric shower.They have a dual RCd CU and apparently all earthing is up to date,Has anyone come across this before ? Any advice on where to start looking. Any advice on finding this fault woluld be much appreciated.Thanks
 
What type of shower is it mate. Power shower run by a pump. Gravity fed via tanks in loft? or from a combie boiler? Maybe look at the pipe run but sounds strange if the install is upto 17th and water bonded shouldnt be happening ?
 
Firstly test the Ze on the incomming supply make sure there is no supply fault then do an R1R2 test ,IR test , then Zs , and RCD tests
as you would normally ,check all connections make sure they are tight especially in the shower switch they can come out and generally have a good visual check of the connections

Nick
 
its off combi timo,the main incomer(lead) is earthed to board,but the feed to old copper pipework upstairs is plastic????surely if there was some current leakage the RCD would trip no???
 
its off combi timo,the main incomer(lead) is earthed to board,but the feed to old copper pipework upstairs is plastic????surely if there was some current leakage the RCD would trip no???

Yes the RCD will trip but normally over 15mA and that's quite a tingle!
 
Agree with IQ doesnt take much GEDC4606.jpg
 
One of the reasons why householders and plumber alike should know it's foolish to mix and match between plastic and copper in households, ....or anywhere else come to that!!

First off i would be checking the resistance of that upstairs pipework, it may just be picking up a partial connection with the bonded pipework from downstairs. Then check out any electrical connections at the power shower pump(s) etc!!
 
Thanks all,been today sorted,plasterer had screwed through live on t&e noting else,didnt show up on IR test,leak right above sodden joist making wall,shower live!!!!!!!!THANKS TO ALL AGAIN
 
yes davey d, The IR test on broken cable one minute was >500 then the next minute <50 !!!!!

Have found this a few time myself , normally with a screw bang through the center of the cable !
Makes you think either the meters faulty or you have just lost the plot and forgot how to test !!!
 
there was a similar incident posted here recently

i'm guessing it mightn't show on IR testing if only the phase/line conductor is nicked

when the surrounding area gets wet -i the wall might be 'live'
 
Last edited by a moderator:

Reply to Shower shocks!!!!!!! in the Australia area at ElectriciansForums.net

Similar Threads

Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
732
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock