Discuss Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net

Matters not. I am not saying up the breaker.....but if you do up it, the cable should also be upped accordingly for cable protection. That protection is needed, even though you are not varying the load. Just regulation, that's all.
The regulations specifically allow omission of fault protection where the circuit is not expected to be able to carry overload current so you can have a situation where say a fixed load is 46 amps the ccc of the cable is 48 amps but your ocpd is 50 amps provided fault protection is afforded as required by section 434

The formula for the tabulated current becomes Ib/correction factors rather than In/
 
Last edited:
The regulations specifically allow omission of fault overload protection where the circuit is not expected to be able to carry overload current so you can have a situation where say a fixed load is 46 amps the ccc of the cable is 48 amps but your ocpd is 50 amps provided fault protection is afforded as required by section 434

The formula for the tabulated current becomes Ib/correction factors rather than In/

corrected that for you.no charge. otherwise i agree, as long as the Iz > Ib.
 
Matters not. I am not saying up the breaker.....but if you do up it, the cable should also be upped accordingly for cable protection. That protection is needed, even though you are not varying the load. Just regulation, that's all.
OK then. The circuit is in place, whose to say the load won't be increased in the future?
 
OK then. The circuit is in place, whose to say the load won't be increased in the future?

That's not how you design a circuit though. After all the shower could be removed and a new sub CU installed at the end of the cable if the use for the room changes.

If the load changes, the circuit design changes and protection and cable size should be altered to suit.
 

Reply to Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Replies
4
Views
1K
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
Replies
10
Views
2K
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
Replies
2
Views
213
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...
Replies
8
Views
865

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock