Hello,

Newcomer to the forum, so hello all.

Just to clarify, although I understand most of my way around the regs and workings, still get an approved guy to to any work......just thought I'd get that out of the way!

Anyhow, I have an old property that fed by good old overhead Live/Neutral so have a TT earthing pole.

When the property was renovated, the whole place was re-wired and a new CU was installed. As the meter and fuse is around 4m from the CU, there is also an Type S 100amp RCD incomer protecting the tails to the CU. The CU has been recently replaced as the incomer was tripping and on investigation, it was installed in a strange way, it was a single 30amp RCD CU and the lighting was being protected by the RCD and the socket rings on the non-protected side, hence why the incomer was tripping.

The original CU also had a 40amp mcb providing a feed to another small CU (without RCD) in an outbuilding.

I suspect the fault lies within the outbuilding and of course, the main incomer would trip.

Therefore, the CU has been replaced with a 17th edition one configured in High Integrity with dual RCDs splitting the lights and rings and also an RCBO feeding the outside CU.

However, and yes, I finally get to the question!....... As this RCBO is single pole, am I correct in thinking that if there is a N-E fault then as the RCCB is single pole it might not trip and still cause the incomer RCD to trip instead taking out the whole CU. Or should the RCCB still trip out first?

We had a trip yesterday where again the main incomer RCD tripped. This is causing a big issue as we have a monitored alarm which is losing power. It's battery backed up, but if we are away for a few days will cause the battery to drain and has actually destroyed a battery in the past.

It could just be a faulty Type S 100ma RCD (it does tend to buzz on high throughput) as there is never a common reason for it to trip, or am I right in my thinking that as a Single Pole RCBO doesn't break the Neutral (and remember is on a TT system) which could cause the incomer to trip.

Many thanks for your help in advance.
 
Last edited by a moderator:
Yes it is, it's a British General one - BG Electrical

So personally, I would of thought that if there was a N-E fault then it would still trip, but because the N isn't being broken, the RCD would also trip. However, it doesn't, just the RCD trips.
 
RCBOs should never be used on installations where time delayed RCD protection has been used between it and the source of supply unless they are double pole or single pole switched neutral. Single pole will not do (which the majority or RCBOs are).

Edit: For the avoidance of doubt, I removed reference to upstream/downstream.
 
Last edited:
Thanks D Skelton, this is what I was assuming. However, if there was a N-E fault, am I correct in thinking that the SP RCBO should still trip along with the RCD? I thought a SP RCBO still trips with a N-E fault, but of course, not breaking it, hence the time delay RCD then tripping. Luckily, there is enough room in the CU to fit a double sized DP RCBO, can't put a single sized DP in there as it needs to go on the Buzz bar
 
A SPSN RCBO down stream will be fine unless a two phase supply is involved, the RCD part of the RCBO will still Detect a N-E fault the Switched N will disconnect it.

Edit: see^^ #5
 
Last edited:
Define upstream/downstream??

I say downstream is towards the supply, upstream is towards the load.

You get my point.

Is 5th gear in a car a high gear or a low gear?
 
I see what your saying, I just thought you had read it wrong...
upstream to me has always ment to the origin... But that could just be me

No lol, I didn't read it wrong, as you say, my definition of upstream/downstream is clearly different. I've edited my post to remove doubt.
 
Okay, semantics aside, assuming a DP S-Type RCD up-front ;-), why is a SPSN RCBO not suitable closer to the load in single Phase situations ?
 
i always refer to downstream to be the load end. current flows from source to load, same as a river flows from source, so up is the supply end, and down is the load end.
 
Okay, semantics aside, assuming a DP S-Type RCD up-front ;-), why is a SPSN RCBO not suitable closer to the load in single Phase situations ?

In the event of a neutral to earth fault the single pole RCBO will trip but not clear the fault and so the DP RCD will trip.

Whilst not breaking any regs it messes up any discrimination you may want!
 
In the event of a neutral to earth fault the single pole RCBO will trip but not clear the fault and so the DP RCD will trip.

Whilst not breaking any regs it messes up any discrimination you may want!


SPSN = Single Pole Switched Neutral in this context, I am aware SPSN could apply to single pole SOLID Neutral types too though :)
 
SPSN = Single Pole Switched Neutral in this context, I am aware SPSN could apply to single pole SOLID Neutral types too though :)

No, the nomenclature is pretty well defined.

SP (or SP+N) single pole (solid neutral)
SPSN single pole switched neutral
DP double pole
TP triple pole
TPN (or TP+N ) triple pole solid neutral
TPSN triple pole switched neutral
 

Reply to Single Pole RCBO in TT with Time Delay RCD Incomer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
751
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
913
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock