I see what your saying, I just thought you had read it wrong...
upstream to me has always ment to the origin... But that could just be me

No lol, I didn't read it wrong, as you say, my definition of upstream/downstream is clearly different. I've edited my post to remove doubt.
 
Okay, semantics aside, assuming a DP S-Type RCD up-front ;-), why is a SPSN RCBO not suitable closer to the load in single Phase situations ?
 
i always refer to downstream to be the load end. current flows from source to load, same as a river flows from source, so up is the supply end, and down is the load end.
 
Okay, semantics aside, assuming a DP S-Type RCD up-front ;-), why is a SPSN RCBO not suitable closer to the load in single Phase situations ?

In the event of a neutral to earth fault the single pole RCBO will trip but not clear the fault and so the DP RCD will trip.

Whilst not breaking any regs it messes up any discrimination you may want!
 
In the event of a neutral to earth fault the single pole RCBO will trip but not clear the fault and so the DP RCD will trip.

Whilst not breaking any regs it messes up any discrimination you may want!


SPSN = Single Pole Switched Neutral in this context, I am aware SPSN could apply to single pole SOLID Neutral types too though :)
 
SPSN = Single Pole Switched Neutral in this context, I am aware SPSN could apply to single pole SOLID Neutral types too though :)

No, the nomenclature is pretty well defined.

SP (or SP+N) single pole (solid neutral)
SPSN single pole switched neutral
DP double pole
TP triple pole
TPN (or TP+N ) triple pole solid neutral
TPSN triple pole switched neutral
 

Reply to Single Pole RCBO in TT with Time Delay RCD Incomer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
845
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
965
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock