See the smiley on the end Dave :), what with the earlier semantics, plus a discussion on the IET site I was involved in the other day someone else made the point that SPSN could apply to solid N types :)

Semantics, shemantics lol
icon6.png
 
Is it not 1P RCBO means fixed neutral and only operates Line conductor
1P+N RCBO means RCD part operates the line & N but overload only operates line not Neutral
 
Last edited:
Thanks for all your help guys.

The RCBO is just a single pole so I'm organising it to be changed to a double pole. Luckily there is space in there for a 2 unit one.

I'm beginning to suspect that the time delay RCD is a bit trigger happy (faulty) so I'm getting that swapped out too.
 
SPSN and SP+N mean the same thing!! I have always used the term SP+N myself when describing SP RCBO's that switch the neutral as well as the line conductor.... Basically boils down to different manufacturers using one or other of the above terms....
 
And you're basing that suspicion on what? A hunch?

Maybe testing it would be the way to go first? But then what do I know?!

He hasn't tested anything, because he is a telecoms technician and hasn't the test equipment to test the existing installation. So he's first course of action should be to get this electrician he talked about in to check/test the installation, especially the existing RCDs and to then listen to the advice of the electrician as to what needs to be done to rectify his present situation. He can always come back to check/confirm the electrician advice.

This thread should have been posted in the DIY section....
 
SPSN and SP+N mean the same thing!! I have always used the term SP+N myself when describing SP RCBO's that switch the neutral as well as the line conductor.... Basically boils down to different manufacturers using one or other of the above terms....

The SP RCBO only switches the live, and should not be used on a TT system.
There is a SP with solid neutral (this the common one) & SP with switched neutral.
& yes manufacturers do label them with differing terms.
 
Yes, of course it'll all be tested out, I was just satisfying my thoughts around it all. Although I'm not going to replace/test anything, its good to be clued up on what's going on. I didn't put it in the diy section as this certainly isn't diy. I'm getting it all checked later this evening.
 

Reply to Single Pole RCBO in TT with Time Delay RCD Incomer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
751
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
913
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
1K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock