See the smiley on the end Dave :), what with the earlier semantics, plus a discussion on the IET site I was involved in the other day someone else made the point that SPSN could apply to solid N types :)

Semantics, shemantics lol
icon6.png
 
Is it not 1P RCBO means fixed neutral and only operates Line conductor
1P+N RCBO means RCD part operates the line & N but overload only operates line not Neutral
 
Last edited:
Thanks for all your help guys.

The RCBO is just a single pole so I'm organising it to be changed to a double pole. Luckily there is space in there for a 2 unit one.

I'm beginning to suspect that the time delay RCD is a bit trigger happy (faulty) so I'm getting that swapped out too.
 

Reply to Single Pole RCBO in TT with Time Delay RCD Incomer in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
845
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
962
Hi all Now being upfront I am not a sparks. I am about to have some work done by a friend (certified) and as he is doing me a favour I want to as...
Replies
5
Views
2K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock