Discuss Sizing DC cables, PV Array to Inverter. Confused. Help please! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

the volt drop is negligible particularly on this system because the voltage is so much higher than standard AC runs.

I've often seen this repeated in this forum but it depends totally on the array design.

Many 230 - 250W panels have 60 cells and so a Vmpp in the region of 30V. A 4kw array divided into 2 strings of 8 will therefore have string voltages of 240V and (neglecting skin effect losses on AC) for the same cross-section the AC and DC losses per m of cable will be much the same.
 
I've often seen this repeated in this forum but it depends totally on the array design.

Many 230 - 250W panels have 60 cells and so a Vmpp in the region of 30V. A 4kw array divided into 2 strings of 8 will therefore have string voltages of 240V and (neglecting skin effect losses on AC) for the same cross-section the AC and DC losses per m of cable will be much the same.
but on this system the voltage in operation will be somewhere between 350-400V, and most of the systems we design are in this range as this is the peak operating range of the inverters we use (and most inverters on the market).
 
but on this system the voltage in operation will be somewhere between 350-400V.

Sorry, I was thrown off the scent by screwdriver's assumption of 30V per panel.

But I don't think you would get away with 4mm^2 in this instance because as the OP says it is a 150m run (so it is "in a field" to quote your earlier posting).

Maybe someone should do the definitive calculation using all the right figures to put us out of our misery.
 
... Maybe someone should do the definitive calculation using all the right figures to put us out of our misery.

Here you are, now I understand which figure is which (NO thanks to the DTI guide, but many thanks to others on this forum) it’s easy:

Total current at max power, where panel Imp = 4.94A, 4.94 x 2 x 1.25 = 12.35A
Total voltage at max power, where panel Vmp = 50.6V, 50.6V x 8 x 1.15 = 466V

Total Isc where panel Isc = 5.35A, 5.35 x 2 x 1.25 = 13.4A (As Screwdriver said, we can all agree 10mm can handle this without getting out our tables!)

Total Voc where panel Voc = 60.5V, 60.5 x 8 x 1.15 = 560V (SWA 600/1000, no problem)

Cable volt drop calculation for the 165m DC run (now measured accurately) on 10mm 4-core (4.7 mA/V/m) is:

Vd = 4.7 x 165 x 12.35 / 1000 v = 9.58V

9.58/466 x 100% = 2.06%

So, as my gut was telling me all along, 10mm is fine.

Compared with running AC for 165m, engineering an AC volt drop of 1% max to prevent over-voltage tripping, it’s a huge saving in copper (and hence cash!).

I rest my case as to which option is better.

I just ordered 4-core 10mm at £4.07/m and some 16mm 4-core (for something else) at £5.68/m. Was I ripped off?
smile.png


ps. I initially thought one uses a different Vd formula for DC. I was confused, and using Ohms/km rather than mA/V/m, and reckoning you had to double the cable length. The latter already takes account of the return path, and apparently reactance and capacitance in big-CSA cables, which is negligible for the smaller stuff, so the single phase figure can be used for DC. Please tell me if this is wrong!

Also, the calc above does not take account of any cable temp factor. Again, it’s negligible and not worth bothering with in this case since 10mm is clearly within spec.

I’m bored with all this thinking now. I’m going out to dig holes instead :)

Thanks, gentlemen, for all you helpful comments.
 
Last edited:
Here you are, now I understand which figure is which (NO thanks to the DTI guide, but many thanks to others on this forum) it’s easy:

Total current at max power, where panel Imp = 4.94A, 4.94 x 2 x 1.25 = 12.35A
Total voltage at max power, where panel Vmp = 50.6V, 50.6V x 8 x 1.15 = 466V

Total Isc where panel Isc = 5.35A, 5.35 x 2 x 1.25 = 13.4A
Total Voc where panel Voc = 60.5V, 60.5 x 8 x 1.15 = 560V

Cable volt drop calculation for the 165m DC run (now measured accurately) on 10mm 4-core (4.7 mA/V/m) is:

Vd = 4.7 x 165 x 12.35 / 1000 v = 9.58V
I don't think this is quite right, 12.35A is for both strings (are you connecting them in parallel at source and if so why the four-core cable?), and also includes the 1.25 safety margin which you don't need when calculating voltage drop at Impp. This will put the volt drop down by at least 20% and possibly a further factor of two.

9.58/466 x 100% = 2.06%

Again, the 466V includes a 1.15 safety margin, removing this will put the actual % volt drop up by 15%.
 
Last edited:
I don't think this is quite right, 12.35A is for both strings (are you connecting them in parallel at source and if so why the four-core cable?), and also includes the 1.25 safety margin which you don't need when calculating voltage drop at Impp. This will put the volt drop down by at least 20% and possibly a further factor of two.

Two strings of 8, paralleled at source, hence 2 x the current. Then the whole damn thing again for feeding into the second phase. Hence the 4-core.

Good point about ‘ignoring’ the safety factors. Thanks!

Again, the 466V includes a 1.15 safety margin, removing this will put the actual % volt drop up by 15%.

OK, understood. So is this (finally!) right?:

Vd = 4.7 x 165 x (4.94 x 2) / 1000 v = 7.66V

7.66/(50.6V x 8)x 100% = 1.89%
 
And, for 6mm (7.9mA/V/m):

Vd = 7.9 x 165 x (4.94 x 2) / 1000 v = 12.88V

12.88/(50.6V x 8)x 100% = 3.2%

With a bit of jiggery-pokery with thermal coefficients, and the argument that this amount of energy would only pass at the very best times, it could be argued that 6mm is fine too. I wouldn’t bother, since the cable cost differential is probably not worth the losses over 25 years, but there it is. It could make a difference to profit on a commercial job.
 
Sorry, I was thrown off the scent by screwdriver's assumption of 30V per panel.

But I don't think you would get away with 4mm^2 in this instance because as the OP says it is a 150m run (so it is "in a field" to quote your earlier posting).

Maybe someone should do the definitive calculation using all the right figures to put us out of our misery.
ah right, I did look, but missed that bit.
 

Reply to Sizing DC cables, PV Array to Inverter. Confused. Help please! in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All, I'm seeking some advice about a solar PV system we had installed in November 2014 please. After 18 months, we seem to be consistently...
Replies
15
Views
6K
crossplot
C
D
Solar panel details Hello everyone Im a new member to the forum, i have done a course on industrial electronics so im no expert on solar panel...
Replies
2
Views
1K
Dougy
D
C
Hi all, This is the first on-grid system I design and install. I live in Amman-Jordan but here we follow same UK standards so basically we have...
Replies
7
Views
7K
Guys, As we know, for switches/cables/isolators etc, you need to multiply your Voc values by 1.15 and Isc values by 1.25 to calculate the...
Replies
7
Views
1K
1
Does anyone know which table I should be looking in to calculate the current carrying capacity of 4mm PV cable and also how to do the derating...
Replies
1
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock