Currently reading:
Smart Board Projectors

Discuss Smart Board Projectors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

moose

-
Reaction score
27
Can anybody please help me as im one who does try to do the job correctly, but im unable to find the correct answers anywhere.

The issue is this, i have tested a number of Smart board Projectors and the readings are example of 4.

1 - 3.4mA
2 - 3.6mA
3 - 3.2mA
4 - 3.6mA

very close to the common 3.5mA, i would fail two of these projectors, but im thinking there is a get out clause maybe, like its about 5mA or upto max 10mA for projector or maybe rely on RCD protection been hard wired as well

number 2 is plugged in to a socket above the ceiling and 4 is hard wired to a Spur.

Could you direct me to some figures not say so please as gaffas need answers not jack said hehe. :)

Thanks guys for you time here..
 
you can't fail them. all this type of equipmwnt has a small leakage. just like computers. that's why you should only wire a limited number to each RCD/RCBO.
 
Well I can if I dont get the right answer to be honest, as testing the projector as an item comes in at 3.6mA which is a fail for an appliance, can you explain your answer better telectrix.

I know about Ring circuits and making clean earth to help etc. RCD ratio(mA stuff lol) for circuits but im looking how not to fail the projectors as an item doing PAT testing..
 
Tels point is you cant have to many items that have a leakage to earth i.e projectors and computers on 1 circuit as the accumulative leakage could take it over the 30 m/a threshold
 
Well I can if I dont get the right answer to be honest, as testing the projector as an item comes in at 3.6mA which is a fail for an appliance, can you explain your answer better telectrix.

I know about Ring circuits and making clean earth to help etc. RCD ratio(mA stuff lol) for circuits but im looking how not to fail the projectors as an item doing PAT testing..

Have you read the BGB Reg 543.7.1.101? Have you tried using an earth leakage clamp meter on the equipment you are testing? your PA Tester may be giving you a duff reading
 
How old are these projectors???
Surely all 4 of them are not up the ****ter !!!
I know you said you would fail 2 of them but the others are pretty much the same.
I wouldnt mind betting if you tested them several times you would get different readings and the other 2 would possibly fail aswell.
Anyway pop a pass sticker on and go to sleep !!!:sifone:
 
If it's over 3.5 ma and below 10ma then it should be on it's own circuit
 
Thats the funny bit quite new thats why i was wondering if they have a designed leakage but was not sure, and if anyone had the same issue with the projectors, ive asked a few friends they get about 2.6mA for their readings from memory.

as for own circuit well ive never seen that so far from any ive seen nore been told by architect, while designing a class room etc.

Thanks for your great push questions and trys so far guys.

will get on tomorrow see if you solve my silly dillema. :)
 
Thats the funny bit quite new thats why i was wondering if they have a designed leakage but was not sure, and if anyone had the same issue with the projectors, ive asked a few friends they get about 2.6mA for their readings from memory.

as for own circuit well ive never seen that so far from any ive seen nore been told by architect, while designing a class room etc.

Thanks for your great push questions and trys so far guys.

will get on tomorrow see if you solve my silly dillema. :)

May be they don't design the classrooms with Smart Boards as the main factor, the Regs do state the requirements as I have already posted
 
It's all well and good quoting regs about how things should be installed, but it appears to be irrelevant to the question.

The OP has asked about appliance earth leakage when carrying out a portable appliance test.
 
Can anybody please help me as im one who does try to do the job correctly, but im unable to find the correct answers anywhere.

The issue is this, i have tested a number of Smart board Projectors and the readings are example of 4.

1 - 3.4mA
2 - 3.6mA
3 - 3.2mA
4 - 3.6mA

very close to the common 3.5mA, i would fail two of these projectors, but im thinking there is a get out clause maybe, like its about 5mA or upto max 10mA for projector or maybe rely on RCD protection been hard wired as well

number 2 is plugged in to a socket above the ceiling and 4 is hard wired to a Spur.

Could you direct me to some figures not say so please as gaffas need answers not jack said hehe. :)

Thanks guys for you time here..

May be getting into trouble here, but why do you say 3.5ma is the cut off point for failure?
 
Since leakage to earth is not really covered in in service testing and he is using a PAT tester I would assume he is measuring the protective conductor current or touch current in accordance with the COP. which is the current that does leak to earthed parts.

In answer to the original question, there is not really any "get out clause". I would just say make sure you are testing correctly and see if you get different values, it is a bit of a pass fail situation for in service testing. But 3.5mA does seem a bit high for a smart board projector, they may be just a cheap power supply.
 
Thanks for the great response to my main question, so the conclusion we all seem to agree is the projectors for the smart boards maybe, failing due to the readings given.

3.5 is a fail for class I equipment and no exceptions (not counting Heaters 3.5/5mA).

I like the idea of a bad power supply, this guides me to a reason, the tests where constant, as I tested 3 times and the readings did not change on three accounts.

Tester was a Martindale 2100.

Thanks again for the good advice.. :)
 

Reply to Smart Board Projectors in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock